    Daikin RTD-20



    Has anyone any experience of operating a Daikin ERQ condenser connected to an AHU via a Daikin RTD-20 interface? The system is cooling only (with separate heater battery), Daikin expansion device with controller. I've wire as per available diagrams - closed run input to S0/S1, 0-10vdc capacity input to S0/S3. The condensing unit will just not start up?? Is there a recommended commissioning step procedure?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin RTD-20

    The RTD 20 needs to operate via Modbus from the BMS.
    There are 2 types of control box on the Daikin AHU set up. 1 controls via 0-10v dc input and the other via a digital input leaving the capacity control on the pipe sensors. You should be able to disconnect the RTD and get the system operating by shorting the DI terminals and connecting a PP9 across the 0-10v terminals.

    The RTD just allows remote control and adjustment of set points from afar.

    Have you connected a BRC controller?

  3. #3
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Daikin RTD-20

    Hi Frank, how does the RTD communicate with the control box? The only cable connecting the two is the power supply cable? I've a feeling that I've been supplied with the wrong control box which needs a r/c fitted as you suggest. I did connect a r/c and an air thermistor into initially to get it tested and refrigerant charged, but then disconnected these and connected the RTD module - now it don't work the designer says it should run of the 0-10 input as mentioned - Im beggining to think the control box I have is not capable of this. If I do use the brc instead can I switch it on off via the t1/t2 input or will I need a KRP board also??

  4. #4
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: Daikin RTD-20

    1. Make sure correct capacity plug is connected to indoor control panel
    2. Installed BRC (leave RTD offline) and carry out test run operation - outdoor unit/with AHU fan operation
    3. Once test run complete, connect RTD-20 with power supply and P1-P2
    4. Set ERQ mode - Dip switch 1 & 2 ON
    5. Plug the ON/OFF and 0-10V capacity control plug