    Cooling capacity??



    Any1 have an idea how to calculate the cooling load required on a machine like this??? Got a twin evaporator approx 5ft long and 8inchs high. Also has a small evap under thats approx 16inchs x 12inchs.
    image.jpg



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Cooling capacity??

    comp name plate, or tev orifice size

  3. #3
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: Cooling capacity??

    Compressor is an aftermarket 1 that i think is to big to suit thats why i ask. Pipes have been extended and the condensor is now outside.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Cooling capacity??

    ask manufacturer? - last resort, maybe go off pipesizes on internal cabinet, compare to condensing unit spec lists- circuit breaker size will give you a rough idea, fitting a remote condenser would req a higher displacement than the integral but pipe sizes would req increasing and a low ambient kit would be recommended

  5. #5
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: Cooling capacity??

    Ive searched all over no plate with manufacturer on it. The pipes at condensor are 5/8 and 3/8 then reduced to 1/2 and 1/4. The condensor fitted is blue star
    image.jpg

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Cooling capacity??

    If you Google your blue star model number you can download the tech details from Danfos, price of cake.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Cooling capacity??

    http://www.elektronika-sa.com.pl/tcl...MGZ-2001&LID=2

    You'll need to over size, that design is inefficient as feck, fit TEV to other coil, control condensing unit off display thermostat.
    Mostly found in the southern part of this green and pleasant land.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Cooling capacity??

    Hi Harry,

    As you posted this in the A/C section and are talking about cooling load, I assume that you want to calculate what size A/C you need to install in the room where this is fitted?

    If so, providing this display unit is operational at the moment, the only thing you need to look at is its energy consumption. A clamp meeter on the power supply will give you an one of reading and a logging amp meeter will give you both peak and average readings whilst an energy meeter will give you the consumption over a couple of days.


  9. #9
    Join Date
    Sep 2014
    Location
    united kingdom
    Posts
    6
    Rep Power
    0

    Re: Cooling capacity??

    Well, I recommend to Google using your blue star model number. It will give all tech details.