    P8 message on Control Board Mitsubitsh mr Lim



    Hello
    I am servicing a unit(Mr. Slim) which is a ductlee made by Mitsubitch. The control board (thermostat) displays the code P* does any one what is that
    Thanks



  2. #2
    chilled2005's Avatar
    chilled2005 Guest

    Re: P8 message on Control Board Mitsubitsh mr Lim

    hiya i think p8 is a pipe sensor fault, dont hold me to it but im quite sure off the top of my head...its either faulty or not there at all or not sensing the temperatures its looking for e.g. short of gas...

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: P8 message on Control Board Mitsubitsh mr Lim

    Last edited by frank; 25-04-2006 at 07:33 PM.

  4. #4
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    240
    Rep Power
    19

    Re: P8 message on Control Board Mitsubitsh mr Lim

    is a p8 fault just not an outdoor fault?

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: P8 message on Control Board Mitsubitsh mr Lim

    P8 means "Abnormality in Outdoor Unit"

    Possible causes

    1 Wrong wiring of Indoor/Outdoor connection
    2 Reverse Phase
    3 Protection Device operated
    4 damaged Outdoor coil thermistor

    Areas to check

    1 Check continuity of the interconnect wiring - look for breaks (I've had it where rats have chewed the wiring before )

    2 Check the phase rotation - has any work been done on the unit mains wiring?

    3 Has any safety activated? Compressor klixon? LP switch? HP switch, Fan overload? etc.

    4 Measure the resistance of the coil sensor

    If you are still struggling then give Mitsi Technical a ring 08703000300

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: P8 message on Control Board Mitsubitsh mr Lim

    A list of Mitsi fault codes is available here:-
    http://airconwarehouse.co.uk/Techmanuals.htm
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Trane HP Defrost Board Problem
    By FastEd in forum Heat Pumps
    Replies: 8
    Last Post: 05-09-2008, 01:30 AM
  2. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  3. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 02:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •