    R407c



    Anyone out there run across any new machine running R407c?
    Any retros and experience with the stuff? Supposed to be close
    to R-22 properties, haven't checked yet to see what it's about.
    Seems to be an upcoming choice here in the states for R-22 chiller
    type applications.

    Mike Hopkins



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    My firm has installed quite a few DX split A/C units running 407c without too many problems.

    Quality of brazing and flare joint are of prime importance to reduce leakage. I know that is good for any job but these new gases with their smaller molecules really seek out the holes.

    I've found some condensing units tripping out on high pressure during our feeble UK summer but that was down to slightly dirty condenser coils. I also think that the manufacturer was rather mean with his sizing of the coils/fans but could have been a 'one-off'.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Thumbs up

    R407C tends to run with a slightly higher head pressure than R22, typically (30PSI higher) although the suction stays about the same.
    As its a refrigerant mix the local conditions need to be taken into account when using R407c, due to the change in the characteristics of the system as the higher boiling point refrigerants in the mix reach their lowest point and the lower boiling point refrigerants come to the fore. In lower ambients ie UK, Canada ect head pressure control is a definate requirement reduce the likelyhood of the evaporator freezing.
    As regards to retrofitting R22 systems with R407C then that is ok as long as the compressor/ system is charged with polyolester oil and any seals ie in the TEV's ect, are compatible. If the system contains mineral then use CARE 50 otherwise you need to remove all the oil - with a maximum of 5% mineral by volume.
    The cardinal rule here is DONT MIX Mineral Oil and R407C
    An R22 system converted to R407C will have a performance drop of about 4%

    I hope this ain't too long winded lol

  4. #4
    Join Date
    Oct 2001
    Location
    Georgia, USA
    Posts
    58
    Rep Power
    23

    407C

    Not long winded at all by my standards. Appreciate the input.
    What is this CARE stuff I have seen you fellas talking about, I am not familiar with it. Oil I assume maybe POE but what viscosity, grade, manufacturer, etc.

    Mike Hopkins

  5. #5
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    The oil is POE, from memory SW32 or there abouts, whose depends on the manufacturer. ICI Emkarat is one supplier.
    As to care thats a range of refrigerants based on hydro carbon mixes and produced in the UK by calor. It tends to be as efficient as its HCFC equivalent while requiring a lower charge volume, Care 50's charge being around 40% of R22's.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Hi Mike

    We've been using R407c kit for quite some time now and in fact is is getting hard to get R22 kit.

    NEVER installed R22 kit converted to 407 as this really is a no no. How can you get all of the mineral oil out of a system? and be sure that the 407 doesn't mix with it?. Also, as 407 is a blend the equipment should be purposely made to suit to prevent glide.

    When installing 407 kit there is not a lot of difference apart from ensuring clean tools and making extra sure the the system is not left open to absorb moisture as just a small amount can be fatal to the compressor. Efficiencies are about 5% less than 22 with air con systems and efficiencies really drop off with evaporating temperatures below freezing so it is not really suitable for cold work.

    We went on a training course with Mitsi recently and the tutour was saying that before they had purpose made kit they were retrofitting r22 systems to 407. This was achieved by drilling a hole in the base of the compressor to drain the oil before plug welding the hole and charging with 407 - can you believe this??

  7. #7
    Join Date
    Oct 2001
    Location
    Georgia, USA
    Posts
    58
    Rep Power
    23
    Frank,
    I was thinking along the lines of machines out there already
    factory charged with poe oil running R22 and converting to R407C
    down the road. Sorry for confusion there. The CARE refrigerant mentioned sounds like some of the refrigerants we have over here that can run with mineral oil. They aren't cheap though, one we have used rather regular for R12 drop in (so to speak) with out pulling mineral oil is around 9-10 US dollars a pound. I have also seen the filter drier manufacturers coming out with enhanced moisture capacity cores specific for HFC and poe oils. I think if I went to the trouble of welding on a hermetic (assuming) it would be to weld an access valve on the base so one could change the oil too at a later date. Those poe oils aren't cheap either, probably still paying for R&D on them or maybe higher refinement cost, quality.

    Mike Hopkins

  8. #8
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    There is no problem converting equipment or R22 to R407c as long as the system is charged with POE.
    If you want to change a system with mineral oil then you have to get it below 5% mineral before you add the R407c. At the same time its better to replace the compressor.
    There are blends out there which are a direct replacement no matter which oil is used but they are expensive.

Similar Threads

  1. P/h chart for R407c
    By Coolie in forum Technical Speculations
    Replies: 4
    Last Post: 29-05-2011, 06:17 PM
  2. R407C to R404a
    By MaDiNfO in forum Air Conditioning
    Replies: 10
    Last Post: 30-07-2006, 09:34 AM
  3. Toshiba R407c Reversing Valves
    By Brian_UK in forum Air Conditioning
    Replies: 2
    Last Post: 03-09-2005, 11:22 PM
  4. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM
  5. R407C composition
    By Jai in forum Air Conditioning
    Replies: 4
    Last Post: 01-02-2002, 08:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •