    Hi all. I'm not a refrigeration engineer and I need some help please.
    I bought an ex Sainsburys van fridge box to use as a cold room for my farm shop. It came with some Hubbard wiring diagrams which although are pretty basic, helped me wire it up. I got it running off a new large leisure battery and with the help of a large battery charger, it ran for 2 days but was turned off at night. I kept getting a fault code on the controller which flashed HPS but it carried on running perfectly with temperature going down to 2 degrees, stopping and restarting at 4 degrees with the odd defrost in between. Then I shut it down to tidy up the wiring to the controller which I had left at the length it came with. I shortened it to the length I needed so as to mount the controller where I wanted it. When I went to restart it there was a very loud click and nothing. The controller was showing HPS fault. The loud click which happens every time I tried to start is the HPS switch switching on and immediately switching off again.
    Does any one have any idea what the problem could be.
    Thanks for any help.
    John



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: FZ 114 High Pressure Switch

    Is the fan on the outside part of the unit running from memory it has a plug on it so you can disconnect when removing the cover.

  3. #3
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Yes the fan was running and yes it has a disconnect plug.

  4. #4
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: FZ 114 High Pressure Switch

    That's strange because if it's been off for a while like overnight the head pressure would drop and if it sensed high pressure it would stop and show that alarm you may have a faulty switch but you need to know what pressure is in the system and you are not a fridge engineer with test gauges do not even be tempted to bypass the switch,get a local fridge man out this thing isn't in a hot environment is it giving the condensor a rinse out would do no harm the condensor is the outside bit use a hose and washing up liquid not a pressure washer as that would damage the fins.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: FZ 114 High Pressure Switch

    Hi swissjohn.
    I am with cadwaladr, you seem to be locked out on a H.igh P.ressure S.witch Fault.
    This may be electrical or Mechanical or both?
    I am guessing the click is the compressor or Fan contactor. But the safety circuit is holding off the supply?
    Anyway as suggested contacting a local "Fridgie" is the best bet now.
    Where are you in the U.K. Someone on the forum should respond.
    Grizzly

  6. #6
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Thanks for your replies Cadwaladr and Grizzly.
    What I forgot to mention in my original post is that I had my local man who looks after my shop freezers and chillers out to re gas it (I won't tell you why - it's embarrassing )
    The 12v power cable connects to a largish switch - I'm presuming magnetic, and when I press the on button on the controller the switch is activated and supplies power to the control panel which in turn powers everything that needs power. This is the switch that makes the loud click as it activates and straight away switches off again.
    Because of all the HPS fault codes I had that didn't affect the running and then the final one that stopped it from running do you guys think the switch might be faulty or could it be the circuit board in the control panel. If it is the switch it looks as though I would have to have it regassed again.
    Your thoughts please.
    Thanks. John

  7. #7
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Oh by the way, I'm in skegness.

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: FZ 114 High Pressure Switch

    Hi John.
    A bit far for me then!
    I am intrigued as to what is happening?
    You could have an issue with the supply contactor / largish switch, or it could be a safety / control circuit issue
    as already discussed.
    Maybe the coil in the contactor is faulty or the contacts are pited and were sticking in before.
    Who knows I can think of lots of issues that can be easily eliminated once on site and actually looking at what you have got!
    I think you need your fridge guy back to at least assist with the diagnosis.
    Sorry but the fault showing has a relevance.

    Interesting all the same! Please keep us informed.
    Grizzly

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: FZ 114 High Pressure Switch

    Back again. This switch would not be item 48 would it?
    Grizzly

    Attachment 13738
    1
    3TST024 Cabin Controls
    2
    Need Unit SN# A.C. Motor Plate
    3
    Need Unit SN# D.C. Motor Plate
    4
    2QECFZ1002 Electric Panel
    10
    Need Unit SN# Base
    11
    3CND172 Condenser
    12
    3CVS017 Solenoid Coil
    14
    Need Unit SN# Right Condenser Closing
    15
    2708024 Left Condenser Closing
    16
    3CGT052 Belt 7M=615 (CN7MR615)
    17
    3CGT088 Belt 7M=650 poliflex
    18
    3002083 Case FZ114
    19
    3CMP605 Compressor FRASC.C204 O.ESTERE
    21
    3PMS002 Crunckshaft seal
    23
    3FLT100 Filter 3/8 FSA
    25
    3GRI041 Grid
    29
    Need Unit SN# Humidity Indicator
    32
    3MOR038 Terminal Board
    33
    3MTR090 Electric Motor
    34
    3MTR022 D. C. Motor MP80L 12V G1400 W600
    35
    3MTV090 Fan
    36
    2011090 Separator Bracket
    37
    3PRS040 Pressure Switch Hp
    38
    3PLG075 Pulley D.70 7M D.14
    39
    3PLG074 Pulley D.110 7M OMT
    40
    3PLG121 Pulley D.70 7M D.24
    42
    3RBN102 Shut off valve
    43
    3SRP002 Tank
    44
    2706006 Filter Support
    45
    2700505 Valve Support
    48
    3TLR110 Contactor
    49
    3VRP004 Regulating Valve
    50
    3VLS028 Solenoid Valve
    52
    3SPZ003 Brushes


    3
    3EVP266 Evaporator
    4
    2708042 Cover
    5
    3DDO071 Nut X ATT.O-R 11/16"-16 UN
    6
    3DDO072 Nut X ATT.O-R 13/16"-16 UN
    7
    3BUL058 Thermostatic Valve
    9
    2GUN006 Union 11/16”-16Un(3/8 Or)C.Fl
    10
    2GUN007 Union 13/16"-16UN(1/2 OR)C.FL
    11
    3GRI040 Grid
    12
    3GUR026 Gasket O-R 8x2
    13
    3GUR027 Gasket O-R 12X2
    14
    3INF002 threaded insert M 6
    15
    3MTV077 Fan
    16
    3ORF002 Orifice 01 TEF/Y/X 2
    17
    3RND038 Plain Washer D.6X12
    18
    3SNS061 Thermostat Probe
    19
    2708043 Bracket
    20
    3TPO017 Cap
    21
    3TPO018 Cap
    22
    3VTE195 Screw 6x16
    Last edited by Grizzly; 28-04-2015 at 10:24 PM.

  10. #10
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: FZ 114 High Pressure Switch

    Does this thing run on twelve volts dc or 240 ac ? If 12 are the brushes ok in the drive motor.

  11. #11
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Hi again Grizzly. Yes, that looks like the switch that does the clicking. It is the first thing that has 12v to it all the time. I now know what it's called and thanks very much for taking the time to find and list the exploded diagram.
    Cheers. John

  12. #12
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Hi again Cadwaladr. Yes, it is 12v only and the motor runs fine. I've powered that up directly to test it.

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: FZ 114 High Pressure Switch

    Quote Originally Posted by swissjohn View Post
    Hi again Grizzly. Yes, that looks like the switch that does the clicking. It is the first thing that has 12v to it all the time. I now know what it's called and thanks very much for taking the time to find and list the exploded diagram.
    Cheers. John
    Hi John.
    If I am teaching you to suck eggs then I apologise in advance.
    If the 12v is on one side of the witched terminals then that is to be expected. But if the coil contacts have 12v on then permanently then it is indeed the coil at fault.
    Your move!
    Cheers Grizzly

  14. #14
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: FZ 114 High Pressure Switch

    Apollo thirteen comes to mind on this one ha ha.

  15. #15
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    What I intend to do now is try bypassing the HPS temporarily to see what happens. If it fires up and runs ok then by my thinking it shows that the HPS is at fault and vice versa.
    The Contactor has power going in all the time but only activates when I press the Go button on the controller. So there must be power going through to the CPU circuit board for the Controller to function. If the HPS is not at fault then it must be either the Contactor coil OR the CPU Circuit board. But which one?????
    Talking to you two on here helps me think things through and writing my thoughts down helps as well.
    So thank you both for bothering to help.
    I will report back and let you know what happens. It won't be tonight because I have to go to the wholesale fruit market which is in Hull, 70 miles away. No sleep tonight!!
    Thanks again guys.
    Cheers. John

  16. #16
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Well, it's been a busy weekend in the shop so could only have a look today. Did what I said I would - bypassed the HPS and guess what - it works. Runs like a dream.
    Now, I know that I shouldn't do it, but I really think it is just the switch. I only had it regassed just before the problem occured and as I said earlier, I kept getting HPS error messages with no sign of a problem. I now have to source a new HPS and get my fridge man out to fit it and regass it again. I will do this as quick as I can BUT I need to run it during the day to keep my stuff fresh. What do you two think? Can I risk it? What is the worst that can happen? Apollo 13 cadwaladr - thanks for that!!!!!!
    Cheers. John

  17. #17
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: FZ 114 High Pressure Switch

    Give that condensor a wash for sure,desperate times call for desperate measures changing the switch will mean no loss of gas because there should be a Schrader valve but make sure you have a spanner on the stub it fastened to.

  18. #18
    Join Date
    Mar 2015
    Location
    England
    Posts
    9
    Rep Power
    0

    Re: FZ 114 High Pressure Switch

    Thanks for the tips - will do! So it's not going to do an Apollo 13 on me??? Its been running perfectly all day today but switched off for the night.

  19. #19
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: FZ 114 High Pressure Switch

    You could order the part and fit it yourself do as I told you with holding the fitting on the pipework,Hubbard will charge you a pretty penny but may save paying your fridge man another callout.