    Faulty Inverter PCB Daikin VRV-3



    Just replaced for the 4th time the inverter PCB in my Daikin Inverter VRV-3 Model RXQ12P. Sick of spending money. Anyone here can help me to troubleshoot the inverter board as in which component to replace or which component normally fails. No schematic found online
    Attached Images Attached Images



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Faulty Inverter PCB Daikin VRV-3

    How long does the unit operate correctly between changing the inverter PCB's?
    Have you used an inverter checker to check the output of the inverter PCB?
    Have the compressor windings been checked?
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Oct 2013
    Location
    singapore
    Posts
    11
    Rep Power
    0

    Re: Faulty Inverter PCB Daikin VRV-3

    Quote Originally Posted by hyperion View Post
    How long does the unit operate correctly between changing the inverter PCB's?
    Have you used an inverter checker to check the output of the inverter PCB?
    Have the compressor windings been checked?
    i have 15 units. so now changing for 4th unit.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Faulty Inverter PCB Daikin VRV-3

    Joe
    Have you considered that invertors DO NOT like unstable electrical supplies and voltage fluctuations.

    Given a 25% plus failure rate my guess is it's not the PCB's that are at fauly!
    Grizzly

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Faulty Inverter PCB Daikin VRV-3

    Check the neutral connections on your power supplies.

  6. #6
    Join Date
    Oct 2013
    Location
    singapore
    Posts
    11
    Rep Power
    0

    Re: Faulty Inverter PCB Daikin VRV-3

    hi. but after replacing the inverter board, i all works fine and i dont have L5 error code. our voltage at this part of the world is 230V 50Hz. so far the 1st unit that i replaced running well over a year and it operated everyday. my guess is not the incoming voltage but some premature failure on the board

  7. #7
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: Faulty Inverter PCB Daikin VRV-3

    Quote Originally Posted by joerocket View Post
    i have 15 units. so now changing for 4th unit.
    Has the compressor windings been checked?
    Has the mains power/neutral been checked?
    Has the crankcase heaters for compressors been checked?

  8. #8
    Join Date
    Aug 2013
    Location
    greece
    Posts
    6
    Rep Power
    0

    Re: Faulty Inverter PCB Daikin VRV-3

    Quote Originally Posted by Grizzly View Post
    Joe
    Have you considered that invertors DO NOT like unstable electrical supplies and voltage fluctuations.

    Given a 25% plus failure rate my guess is it's not the PCB's that are at fauly!
    Grizzly
    THIS +100
    also check the voltage difference in the three phase current. There must NOT be much difference (lets say 10~15 V will be safe)