    HP switch testing



    was just wondering what is the safest and most ideal way of testing a HP switch on e.g a Medium sized Bitzer reciprocating, iv heard of people using hand pump items but do they work ? and how dangerous to close the discharge service valve and checking if the HP will trip? Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: HP switch testing

    Disconnect the condenser fans and it will trip on Hp

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: HP switch testing

    Or you can switch it off and pump it with OFN till the HP trips.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: HP switch testing

    Hi ibrahimus.
    If this is for the insurance / written scheme then talk to the Insurance assessor.
    Most are quite happy to note the operating HP pressure and allow you to lower the HP set point towards operating.
    Noting the actual trip point for their records, some like you elevate away from normal running prior to tripping.
    Which can easily be done as Frank advises by dropping out some or all of the fan fuses / MCB's.

    If this is for your company files then you decide what option to use?
    Please note that mechanical HP switches can be a bitch to reset.
    The nicer and usually acceptable way if system control software permits is to lower the software HP setting. To slightly above NWP. and raise to meet.
    With so many options one should fit?
    Grizzly