    McQuay ALS SE 312.2 XN Tech Manual



    Good morning all,

    Has anyone got or know of how to get the manuals for a McQuay ALS SE 312.3 XN Chiller. I have spoken to Daikin and got nowhere as they do not just give out the information.

    Thanks in advance.



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: McQuay ALS SE 312.2 XN Tech Manual

    Plug the letters ALS in the search box, a few items come up..

    http://www.daikinapplied.com/search.php

  3. #3
    Join Date
    Feb 2013
    Location
    England
    Posts
    8
    Rep Power
    0

    Re: McQuay ALS SE 312.2 XN Tech Manual

    hi jigs, have you got any particular problem you are trying to overcome?

  4. #4
    Join Date
    Feb 2013
    Location
    England
    Posts
    8
    Rep Power
    0

    Re: McQuay ALS SE 312.2 XN Tech Manual

    Hi Jamescomps. Yes I've got a few issues with this chiller unfortunately. There is only one circuit that runs when switched on but only for a couple of minutes. Then shuts down again but no faults come up. The cooling staging is only getting to 8% when this happens. There's also high pressure alarm, evaporator pump alarm, condenser pump maintenance alarm (chiller is air cooled), compressor
    maintenance alarm and 32k clock board fault, I've reset the time and date but that didn't help and it has also decided to go to the year 2041 on its own now. Any help would be appreciated. Thanks.

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: McQuay ALS SE 312.2 XN Tech Manual

    Hi the pump alarms are a software problem, you need to reset the run hours, but even with the alarm on the system will run fine, the hp alarm, check the pressures with guage and if need calibration, calibrate it and also check the fan inverter is working or not, at 9 bar fans come on and then they speed up fully around 14 bar, your hp switch should be around 19 bar,,and compressors maintenance hours are reset through the controller, any problems let us know and I will help you go through the controller

  6. #6
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: McQuay ALS SE 312.2 XN Tech Manual


  7. #7
    Join Date
    Jan 2008
    Location
    qatar
    Age
    51
    Posts
    61
    Rep Power
    17

    Re: McQuay ALS SE 312.2 XN Tech Manual

    thanks bro. good job and keep it up

    TRY TO LEARN MORE ABOUT A/C SYSTEM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •