04-04-2015, 12:32 PM #1
degas one run mitsi multi scm125 6 way
Good afternoon..
Mitsi scm 125 zj standard inverter up to 6 indoor....(6 outputs all same size)
4 indoors are connected, when no 4 is run (and 1.2.3. off) I can hear gas running through coil of no 1, and temp drops on coil from room 22 degrees to 11 degrees on coil.
I can hear all 6 solenoid valves click on startup, .. all at very different loudness though.
I want to change indoor 1, to the unused connection 6, pipe and interconnect of course, which should sort the problem.
..
Question please....
Can I shut liquid and suction of 2,3,4, start indoor unit 1, shut liquid, then shut suction when pressure near zero,..................... or do I have to recover all refrigerent from all indoors... thank you for reply anyone who knows....
-
04-04-2015, 02:42 PM #2
Re: degas one run mitsi multi scm125 6 way
is it worth trying to swap solonoid heads 5 first, if you do stick it oto another port, make sure you move the interconnecting cable too, best option is to degas it so you can ensure the charge is correct
-
04-04-2015, 04:41 PM #3
Re: degas one run mitsi multi scm125 6 way
Thank you, as my post ill move liquid and suction and interconnect from 1 to 6, There are no leaks on the system the gas charge is correct, the solenoids click on start up... what Im trying to find out is .. can I shut 2 3 4 5 6 liquid and suction lines, start indoor unit 1, shut liquid line and at zero pressure shut suction, rather than pulling all the gas back from all units.
-
04-04-2015, 06:07 PM #4
Re: degas one run mitsi multi scm125 6 way
if you can stick a gauge onto system 1 to see it pump down then yes, then moving pipework onto port 6 you can pressure test and vac that circuit - make sure you stick the blanks over port 1 and label why it isnt used
-
04-04-2015, 08:15 PM #5
Re: degas one run mitsi multi scm125 6 way
thank you fo your help