    York YAES 0595 SB wiring diagram



    Hi guys.
    Maybe some of you has wiring diagram for YAES 0595 SB? Can't sort out inputs for flow switch and circuits remote on-off.
    Cheers



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: York YAES 0595 SB wiring diagram

    i've no wiring diagram, this is from install manual,any good?


    Flow Switch
    A chilled liquid flow switch of suitable type must be
    connected to terminals 13 and 18 to provide adequate
    protection against loss of liquid flow.
    Remote Start/Stop
    Remote start/stop can be accomplished using a time
    clock, manual contact or other ‘voltage free’ contact,
    terminals 15 and 18 with terminals 12 and 15 linked in
    the control section of the control panel. The contact
    must be closed to allow the unit to run. Any time the
    contact opens, the unit will shutdown and the ‘NO RUN
    PERM’ message will be displayed.
    For individual system start/stop contacts connect No. 1
    system to terminals 15 and 18 and No. 2 system to
    terminals 12 and 15. With the associated contact open
    the ‘NO RUN PERM’ message will be displayed and the
    associated systems will not run.
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: York YAES 0595 SB wiring diagram


  4. #4
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    15

    Re: York YAES 0595 SB wiring diagram

    Thank you guys.
    Cheers.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •