Results 1 to 7 of 7
  1. #1
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Red face Inverter Compressor Tester



    Hi all,

    We sometimes get callouts to find a compressor over current fault on inverter heat pump splits. It would be nice to be able to prove the compressor is actually faulty before suggesting we replace it.
    We always do the usual tests, insulation resistance, check windings between each other, has it been tripping the breaker etc.
    We have had situations where clients have requested we replace the inverter module (to save $) before progressing to replacing the compressor. (Obviously we have pre-warned them of the risk they take)
    A few times this has been successful, inverter board replaced, compressor running normal current draw, no more error codes, no call backs.
    Is there a device which we could use to supply a digitally commutated power supply to prove the compressor is actually faulty?
    Please note I am not referring to an inverter board checker with LED`s.
    I am referring to a device to drive the compressor independent of the units control system.



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Inverter Compressor Tester

    can you not buy a normal motor inverter and wire the compressor to it and slowly start it

  3. #3
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: Inverter Compressor Tester

    Quote Originally Posted by martinw58 View Post
    can you not buy a normal motor inverter and wire the compressor to it and slowly start it
    Thanks for the reply Martin
    I will have a ``Google`` around and see what i can find.

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Inverter Compressor Tester

    let us no how you get on

  5. #5
    Join Date
    Jun 2013
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Inverter Compressor Tester


  6. #6
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: Inverter Compressor Tester

    Quote Originally Posted by PMS View Post
    Thank you for the responses.

  7. #7
    Join Date
    Feb 2015
    Location
    uk
    Posts
    36
    Rep Power
    0

    Re: Inverter Compressor Tester

    daikin and mitsi do them as well and fluke do a multimeter that will measure inverted ac current

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •