    compressor cycles per hour question



    Hi all, I'm working on a self-contained custom refrigerated box. Temperatures are ok but it cycles 9-10 times per hour. Cycles on for 3-4 minutes then off 3-4 minutes. I have heard it said that a run time of 18hours per day is about right. There is no history available. R134A. cut in 32°f- cut out 38°. SH-10. ANy suggestions



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: compressor cycles per hour question

    .

    Most compressor manufacturers do not like their comps
    starting and stopping more than 6 times an hour.

    If it is well insulated a fridge should be off for as long as it is on,
    when used as a storage fridge.

    12 hours a day is good, 16 run hours a day means the on to off
    ratio is in the not very economic side but some systems with
    a lot of duty and a lot of through put can run longer and cope ok.

    What you don't want is the compressor chopping in and out.
    It works best when it is running or when it is off, it will fail quicker
    if it is cycling too often.

    Run it longer with a wider control diff and it will stay off longer.

    Rob

    .
    Last edited by Rob White; 12-03-2015 at 03:35 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: compressor cycles per hour question

    If it takes 3-4 min. to cool it down then the unit is too big for the box.
    But you can increase the differential and add a timer or use off delay parameter on the controller to keep it still for 0 min. before restarting.

    Another thing is to check where the temp sensor is located, it might feels cold air from the evaporator outlet while it should be on the evaporator inlet air temp.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: compressor cycles per hour question

    is it actually cycling on thermostat or is the compressor overheat kicking in and then resetting when the body cools down?
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: compressor cycles per hour question

    Think smaller compressor can start 10 times an hour, bigger ones its 6 times an hour, maybe you could fit an anti cycle timer on if it has an electronic controller delayed start may be one of the parameters.
    Mostly found in Oxfordshire, UK :)

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: compressor cycles per hour question

    Perhaps cycle evap fans with temperature controller.

  7. #7
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: compressor cycles per hour question

    I should give you guys the whole scenario. I am trying to build a more energy efficient storage refrigerator. I have modified our standard storage box and as follows.
    1) More insulation with thermal breaks
    2) High efficiency fan motors
    3) Replaced condensate evaporator with compressor hot gas assist condensate evaporator.
    4) Reduced compressor size from our original (designed 10 years ago)

    I have reduced our energy consumption by 24% through these measures, but it is not enough. Due to the case temps being good and the cycle times what they are reducing the compressor size seems to be the next step.

    Yes thermostat sensor is in discharge air.
    I sampled the avg. product temp on all shelves front to back and left to right. High-39.5°f, low-35.9°f = avg 37.5°f this fine.

    which brings up additional questions;

    1. How does reducing the coil size affect running kW if I keep the same condensing unit?
    2. If I change the condensing unit will I need to change the coil too? Is there a way to know?
    3. Any suggestions greatly appreciated.

    I'm am sorry for not being more forthcoming in the first post.