    Question catering freezer confusion!!



    Hi all,
    I'm an air con engineer but was asked to have a look at a catering freezer that was defrosting I turned up to find a completely blocked filter after clearing that the temperature immediately started to drop but only got as far as -4/-5 doesn't seem to be any other problems basically I don't want to fit a line tap if I don't have to. what I'm wondering is could the compressor hold enough heat from running with a blocked filter that the system is still running at too high a pressure to subCool. Basically is it worth turning it off completely for a few hours and starting it up once the compressor has cooled?



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Age
    37
    Posts
    12
    Rep Power
    0

    Re: catering freezer confusion!!

    Filter was on the condenser btw

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: catering freezer confusion!!

    .

    You don't say what refrigerant it is, but if it is 404
    they suffer from Refrigerant thermal decomposition
    (the gas burns out) if the system runs too hot and
    too long with a blocked condenser.

    If the comp is ok it might be the refrigerant, the only
    way to find out is with a set of gauges.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: catering freezer confusion!!

    With a filter on a condenser it could be a Polar or Apollo brand, if so and it is an upright freezer does it have an evaporator coil and fan or do the inside walls freeze up like a chest freezer and has a small circulation fan, if it is the latter then you have to give it time to pull down, also check the door is closing and sealing, I have had worn hinge pin bushes on these, in the past I have had to put a fresh charge of gas in these cabinets as after a while and a few blocked condensers working in high ambient conditions they tend to lose efficiency.

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    37
    Posts
    12
    Rep Power
    0

    Re: catering freezer confusion!!

    Thanks guy's, it is 404 and forced convection on the evaporator pretty sure thermal decomposition will be the problem here then.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: catering freezer confusion!!

    If it has got really hot, then the high head pressure that goes with this can break the valves in the compressor and stop it pumping, it may cool a bit but then stop at too high a temperature.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: catering freezer confusion!!

    probably the condenser is still blocked...

  8. #8
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: catering freezer confusion!!

    Put the line tap on it .You are looking for a diagnosis and agreeing a solution without even putting a gauge on it.

  9. #9
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: catering freezer confusion!!

    Regarding condensers, fridge engineers don't need to be told this, the fins can look clean but deeper in the coil block can still be blocked, we can tell by just feeling the discharge and liquid lines, in this case get your air compressor or bottle of nitrogen on the job or if in a greasy kitchen it will need degreasing, fitting a line tap would be so simple and give you a window of the system.