24-04-2006, 09:36 AM #1
TEV range & minimum pressure diff issue
HI Sirs
Pls give your ideas
Need to select a TEV for a R22 system of capacity 56KW(16USRT)at Te=10C ,Tc=48C. I choose Emerson Alco TEV HFE valves(nominal 15USRT),it's a litter higher than norminal at this condition.
It's a parellel compressor system,while single compressor is working. The capacity is 50% of full load.
If the TEV adapt to the change,the mass flow across the valve decrease and the pressure drop should become small,then the evaporative pressure and condenser pressure difference should be small.
I wonder if there's minimum pressure diff requirement across the valve. if so, can the TEV properly work at 50% loading situation
regards
LC
I hear...I forget;I see...I remember;I do...I understand
-
24-04-2006, 02:59 PM #2
Re: TEV range & minimum pressure diff issue
I have similar situation on Rhoss chiller but compressors in paralell are 120 000 + 160 000BTU.So it can be done.However check with valve company.
Renato
-
24-04-2006, 04:32 PM #3
Re: TEV range & minimum pressure diff issue
Originally Posted by LC
...then the evaporative pressure and condenser pressure difference should be small.
At the same time, the discharge pressure will reduce slightly for the same reason.
The differential pressure the TXV will see does decrease some, but should not significantly reduce the differential pressure or the capacity of the valve.
Similar Threads
-
Liquid Overfeed Systems
By US Iceman in forum NH3Replies: 151Last Post: 08-03-2007, 05:34 AM -
Minimum discharge pressure for ammonia systems
By US Iceman in forum NH3Replies: 86Last Post: 15-01-2007, 04:14 AM -
Screw compressor system losing oil differential pressure
By orm in forum Trouble ShootingReplies: 27Last Post: 27-10-2006, 03:19 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM