    60 HZ connection



    We have to make a quote for 2 splits onboard a Navy vessel on 60 Hz. We want to install a Fujitsu, Mitsubishi or Daikin. Anyone an idea if the standard units we buy in Europe (240/50Hz) can function on a 60Hz main supply?
    Are units for the US different units then?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: 60 HZ connection

    is the voltage in the 60Hz main supply is 240 also
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: 60 HZ connection

    .

    Hello Peter.

    I'm not sure but I have asked one of our technical guys
    and as soon as I know, I'll let you know.

    I don't know why, I feel like saying yes they will work on 60Hz
    but I will find out for you and get back.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: 60 HZ connection

    Yes Peters, no problem with the sort of connection you use, 60hz is not an issue, voltage, no of phases and amp drawing is important.

    Good luck.

  5. #5
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: 60 HZ connection

    The equipment you specify will have to be approved by the vessel insurance. i.e. Lloyds, DNV etc. for marine usage.

    50Hz equipment operates at 20% increase in speed at 60Hz. There is also the issue for 3ph equipment onboard not being earthed and should a hull earth be used is the electronics safe?

    It would be better to ensure equipment is marine grade before quoting as a domestic split will fall apart in a marine environment. The are just not built for harsh environments.
    I love the smell of Ammonia in the morning!

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: 60 HZ connection

    Hi Peter.
    Hooksters comments tell me He has maritime experience.
    I used to work on Marine for J&E Hall and as the equipment supplied was bespoke there was rarely an issue.
    Particularly as Old time (Non Digital) controls where set up in situ. With Step controllers and electromechanical time clocks adjusted to suit. however a 50hz unit will run faster with 60hz.
    Imagine controlling over 24hrs, when the clock thinks approx. 28.8 hrs has elapsed!
    VSD's are another potential issue!
    Bear in mind though a modern digital system is something else.
    You are wise to question this and I would also recommend that you confer with the Manufacturers.
    Most I assume would be able to supply something.
    Grizzly

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: 60 HZ connection

    I've fitted inverter splits to boats before, requested by clients so no come back on us if units failed early, average life span about 4 years, i think a few of them were 60hz but i could be wrong.
    Mostly found in the southern part of this green and pleasant land.

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: 60 HZ connection

    .

    I have had it on good authority that unless specified most AC systems
    are not designed for 60Hz and definitely not for marine applications.

    It's to do with generated 3ph, neutrals and earths.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: 60 HZ connection

    Quote Originally Posted by Rob White View Post
    .

    I have had it on good authority that unless specified most AC systems
    are not designed for 60Hz and definitely not for marine applications.

    It's to do with generated 3ph, neutrals and earths.

    Regards

    Rob

    .
    I dont agree.
    All compressors and fan motors work on both 50hz and 60hz, its only about turning speed and capacity.
    Electronics don't care about hz, it runs on 12vdc or 24vdc.
    Neutral and earth has nothing to do with it.
    The stories about transformers getting hot is an old myth.

    I do agree about the unit enclosure and coils, if you want it to last marine life, it must be built from SS and Titanium.

  10. #10
    Join Date
    Oct 2007
    Location
    sweden
    Posts
    93
    Rep Power
    20

    Re: 60 HZ connection

    Is almost no problem if 50Hz motor running on 60 Hz if Voltage slightly increase, but opposite - running true US manufacture 60 Hz motors/transformer on 50 Hz system can make problem with current rush depend of saturate iron core and unnecessary heating if not take down voltage under 200 Volt (191 Volt)

    many compressors make for international market are designed for using both 50 and 60 Hz environment and have necessary margin for both case.

    If inverter compressor - not care of frequency if going from 50 to 60 Hz (but opposite are different with US-equipment and smaller capacitor inside...) ie. input power rectified to DC and compressor feeds from inverter with different frequency anyway, but control system can struggle and clock going wrong speed and inverter working noisy (if working is noise-optimized to 50 Hz mains but feeded with 60 Hz) if not can select between 50 or 60 Hz using in some menu...

    12/24 Volt?? - I think we talk about much bigger machine than can solve with Danfoss 12/24V small compressors...
    Last edited by xxargs; 16-03-2015 at 04:59 PM.

  11. #11
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: 60 HZ connection

    >

    I have spoken to the manufacturer and the tolerance for inputs
    are well within the limits, but the problem is controlling inverters
    and then earthing and neutrals to them.

    Most AC manufacturers will not give a warranty if used in the marine
    environment.

    That is from the manufacturer themselves, might work, will work but the
    issue, if it doesn't work is the warranty / guarantee.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 60 HZ connection

    Thanks for all the replies so far. The units are Mitsubishi inverter units, so fully electronic controlled and speed is re-generated by the internal power PCB's. So speed will not change I think if connected to a 60 HZ unit. It's onboard a Navy vessel and we don't need special approvals for this. Only the Navy autorities will give it a go for me.
    Capacity we need is 2 x 6 kW (+/- 18.000 BTU) cooling capacity (radar power room)
    We already made a separate offer with a stainless steel enclosure we will make (OEM) for both indoor and outdoor and with 60 Hz Bitzer or Tecumseh compressors.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: 60 HZ connection

    Sounds an interesting job Peter!
    Well Done.
    Grizzly

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 60 HZ connection

    Quote Originally Posted by chemi-cool View Post
    I do agree about the unit enclosure and coils, if you want it to last marine life, it must be built from SS and Titanium.
    This application is for the A960 Godetia Vessel and it will be taken out of service within 5 years. There are standard 60 Hz Panasonic on/off airco's on board inside the ship since 20 years without any corrosion.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: 60 HZ connection

    300px-Godetia_(A_960).jpg

    So that's how you go fishing......

    Best of luck with the project.

  16. #16
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: 60 HZ connection

    Ummmmm, Peter, is it 240V and earth or is it 2 x 120V + earth like we have. Not sure if it matters.

  17. #17
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: 60 HZ connection

    Quote Originally Posted by Peter_1 View Post
    Thanks for all the replies so far. The units are Mitsubishi inverter units, so fully electronic controlled and speed is re-generated by the internal power PCB's. .
    Hello Peter.

    Can you clarify which Mitsubishi.

    Mitsi Electric or MHI?

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 60 HZ connection

    Normally Electrci but we can go also for MHI.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: 60 HZ connection

    Quote Originally Posted by Peter_1 View Post
    Normally Electrci but we can go also for MHI.
    I have it on good authority that MHI will not work under
    those conditions and if by chance they do MHI will not
    guarantee them.

    That is in the UK, it might be different with other suppliers.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  20. #20
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 60 HZ connection

    Thanks Rob
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.