    York screw compressor



    I have been called in to service a York DXS 24 compressor installed on a YCAS chiller. The compressor starts up okay but does not load. While running the discharge temperature keeps increasing until I shut down the system at about 90 Deg C discharge temp. The standing pressure at present is about 7.5 Bar. After starting, the suction drops to about 5 Bar and the discharge goes up to 12 Bar. The oil pressure is about 11.5 Bar. I have replaced the loading solenoid valve and coil and the oil filter. On the side of the compressor there is a large plug which houses an oil non-return valve. This valve has an arrow showing oil flow direction. I spoke to a York Tech who said that maybe the valve was installed in the wrong direction. I turned the valve around but still no difference. Has anyone else had a similar problem and what do I need to check and do to get this system running correctly. This chiller is installed in a Data Centre so I need to resolve this problem soon.



  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: York screw compressor

    High Mike1
    You could have a slide problem i.e. broken slide valve return spring. Do a FLA test it looks like you are not unloading.
    Last edited by hookster; 03-03-2015 at 07:44 AM.
    I love the smell of Ammonia in the morning!

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: York screw compressor

    Do a Google search using the following text;

    york form 230.10 m1 804

    The top few results relate to similar issues..

  4. #4
    Join Date
    Mar 2014
    Location
    South Africa
    Age
    72
    Posts
    19
    Rep Power
    0

    Re: York screw compressor

    Thank you Hookster and HVACRsaurus
    The compressor is definitely unloaded as I am drawing minimum current on start up. I have printed the manual from the web and will trouble shoot accordingly tomorrow.

  5. #5
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: York screw compressor

    Hello Mate
    Tell us more! What was the temperature of the chilled water? You say you you have changed the loading solenoid coil, valve and oil filter, why? Had the coil failed? Have you checked the coils to see if you have power on them when you running? Have you checked if you have power on terminal 17&18 on relay output board 2? Have you tried manually loading with a magnet? Have you checked if there is a change of state on the unloading solenoid? Lift the coil and check if the shaft of the solenoid lifter is ok.

    Let us know how you go.