    Hello,
    In France we have a lot of problem with the evaporator ( by Profroid)
    I want to know what you use of material in commercial and have you the same problem.



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Gaz leakage exchanger

    Some of the Turkish stuff is very poor, paper thin copper, had one case where return bends kept popping, and the Linde internal pipe work on older cabinets, all you can do is re braze them
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Feb 2015
    Location
    Rennes
    Age
    44
    Posts
    10
    Rep Power
    0

    Re: Gaz leakage exchanger

    Thanks for your answer,
    When i have this problem , i have to re braze all exchanger in order to have best result.
    The problem is the brazing and the quality of final assembly.
    In FRANCE with the most super market , contract is all inclusif , refrigerant , oil, material at 3000/5000€ and the labor .
    Yesterday i have a exchanger replacement , outdoor exchanger hitachi air conditioning .
    I was angry because i have to repair the new exchanger , the Cooper like a paper.

    Sorry for my english , i will learn with everybody