    Carrier corrosion



    Anyone had problems with corrosion on the flange connections causing leaks , I think it is due to dissimilar metals , any suggestions ?

    IMG825.jpg
    Attached Images Attached Images
    Last edited by gsracer; 18-02-2015 at 09:40 PM.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Carrier corrosion

    Yes,
    called cathodic corrosion. Dis-similar metals and acidic / PH water levels. Basically ground electrically everything to ground induced voltages. Plus manage water quality and PH as neutral.
    Do a loop impedence voltage check to see what voltages are not being grounded which are creating your problems
    Last edited by Magoo; 19-02-2015 at 02:26 AM. Reason: added

  3. #3
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Carrier corrosion

    Thanks for the reply Magoo . I have considered bonding between the stud and the copper pipe to get them at the same potential . I should have said this is the condenser coil , the only water is rain so it would be difficult to manage the ph value :-)