    Climaveneta Heat pump - Carel alarm



    Can anybody help me solve problem with alarm for Climaveneta heat pump ?

    The model is Climaveneta / MICS-N 0152 - 40 KW

    The machine use controller - Carel Microchiller 2 and when i run it it show alarm A1 (low ambient temperature)

    I set up Antifreeze set point to -10 degree and but again it happen

    The machine use electronic expansion valve Carel



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Climaveneta Heat pump - Carel alarm

    http://www.novatherm.de/f5-edit/ups/...E%20Bedien.pdf
    A1 freeze protect, check pumps,strainer, system has water/glycol in, turn it off and test resistance on sensors to see if theyre all reading similar resistances at ambient temp