    Question UNISAB II - remotely stop/start function over SABCOM OPC Driver



    Hi,

    are there anyone on these forums that knows how I can start and stop the compressor over the Sabcom OPC interface (RS2LAN)?

    My driver is getting all the information from the UNISAB, but I dont know what parameter that starts/stops the compressors.

    I have one parameter that is "Control Mode" but i have problems identifying what the modes are.

    Someone here that have any experience on this topic?



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: UNISAB II - remotely stop/start function over SABCOM OPC Driver

    hi recently I bought 4 sab 128 compressor its control by UNISAB II .

    send your mail , I will send the copy of them.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: UNISAB II - remotely stop/start function over SABCOM OPC Driver

    Hi, nikern

    welcome to RE forums ...

    Quote Originally Posted by nikern View Post
    Hi,

    are there anyone on these forums that knows how I can start and stop the compressor over the Sabcom OPC interface (RS2LAN)?

    My driver is getting all the information from the UNISAB, but I dont know what parameter that starts/stops the compressors.

    I have one parameter that is "Control Mode" but i have problems identifying what the modes are.

    Someone here that have any experience on this topic?
    Control mode can be:
    STOPPED
    MANUAL
    AUTO
    REMOTE

    and all above you can set in ...
    SETUP>CONTROL>COMPRESSOR CONTROL>

    STOPPED
    MANUAL
    AUTO
    REMOTE


    within configuration menu you can set CONTROL ON:

    1. Suction pressure
    2. Brine (measuring water temperature at evaporator output with external PT100)
    3. Discharge pressure
    4. Hot water (measuring water temperature at condenser output with external PT 100)
    5. Ext. cool ....
    6. Ext. heat ...

    To setup point 5 and 6 you need to use manual to set up EXTERNAL INPUT SIGNAL

    Hope this will help a little ...

    Best regards, Josip




    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.