    City Multi Mini Vrf



    Currently installing city multi mini vrf with 4 x PLFY-P20VCM-E2 fan coils each with there own PAR-31MAA remote controller. No bc boxes on system. Just looking for a bit of clarity on addressing of the system i was wondering if it is just addressed like a vrf but the rotary dial sw14 for the branch port is left at '0' and it's just a case of setting sw11 & 12 too 0 1 , 0 2 etc? any feedback appreciated



  2. #2
    Join Date
    Feb 2015
    Location
    UK
    Posts
    30
    Rep Power
    0

    Re: City Multi Mini Vrf

    Unless you are adding the system to an existing central controller and/or interlocking lossnay units and/or using a ME controller (PAR-U02/PAR27), you do not need to manually set the addresses. Leave them all at the factory setting of 00 and it will automatically address. PAR-31s (MA controller) do not need addressing as they are not M-NET controllers, just remember to wire them to TB15.