    Maintence of hermetic compressors



    Long story short, i serviced a unit (puh-4yksa) 2weeks ago and on monday got a call and found the compressor to be locked and tripping mcb... Could i have seen this comming as i have a very un-happy client...



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Maintence of hermetic compressors

    Depends what you did during your service?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Maintence of hermetic compressors

    They can fail like light bulbs, sometimes there is no knowing.

    Few years back i installed a new milk cooler, was there the next day and heard the old ones compressor running, it got a bit slower and slower then HUMMMMMM and silence. Had been running fine to then!
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: Maintence of hermetic compressors

    Done filters,coils,drains,refrigerant charge, check controls, check functions, off coil temp..... What im asking is, if i put a multimeter on to check amps would the compressor being drawing more amps then normal. Or do they just stop????

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Maintence of hermetic compressors

    if the pot was siezing up then you might have noticed increased running current, but might only recognise that if you had previously normal running current (from a previous service)
    the r22 mitsi was out in 1996- so its old, the only protection they have is phase loss, reverse phase and the overload on the contactor, a pitted contactor could cause failure, they also run hot around 80deg, so chances are its circumstantial that you could have predicted the failure

  6. #6
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Maintence of hermetic compressors

    Quote Originally Posted by Harry Trafford View Post
    Done filters,coils,drains,refrigerant charge, check controls, check functions, off coil temp..... What im asking is, if i put a multimeter on to check amps would the compressor being drawing more amps then normal. Or do they just stop????
    How did you check the refrigerant charge?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  7. #7
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: Maintence of hermetic compressors

    Sorry rob badly worded, checked operating pressure. Giving indication that unit has adequate refrigerant charge. Using gauges.

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Maintence of hermetic compressors

    .

    Experience has shown me that Sods law will kick
    in at just the wrong moment. Of all the times when
    that compressor could fail, just after your visit is
    not the best.

    Customer does not understand, so obviously it is
    your fault because it was alright until you arrived.

    Luck of the draw and just explain that it is one of those things.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Maintence of hermetic compressors

    Quote Originally Posted by Harry Trafford View Post
    i serviced a unit (puh-4yksa) 2weeks ago

    Sorry rob badly worded, checked operating pressure. Giving indication that unit has adequate refrigerant charge. Using gauges.
    just seen it's R22 ..Guess what that means..
    Last edited by r.bartlett; 12-02-2015 at 07:58 PM.

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Maintence of hermetic compressors

    Quote Originally Posted by r.bartlett View Post
    just seen it's R22 ..Guess what that means..
    If these checks with gauges were done as Harry says 2 weeks ago then that is Illegal even in Ireland.
    Your a brave man to admit that on this forum Harry.
    The unit is untouchable and basically scrap.
    Over to you Harry!
    Grizzly

  11. #11
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Maintence of hermetic compressors

    Regulations do not prohibit the use of R22 equipment even after the deadline. I would actually argue that still using gauges etc to document operating conditions is less detrimental to the environment than waiting for the complete system leakage to occur.


    I love the smell of Ammonia in the morning!

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Maintence of hermetic compressors

    Quote Originally Posted by hookster View Post
    Regulations do not prohibit the use of R22 equipment even after the deadline. I would actually argue that still using gauges etc to document operating conditions is less detrimental to the environment than waiting for the complete system leakage to occur.


    If the gauges are permanent fixtures then yes you could be correct. However as the law stands you may not fit service gauges unless you are removing the refrigerant charge.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Maintence of hermetic compressors

    EPA guidelines are a little vague on this fitting of gauges, initially we were told only time to fit gauges was if refrigerant was being pulled out, a later briefing from them (verbal) indicated a grey area if the engineer expressed safety concerns with the system, in that instance apparently it may be ok, obviously would need confirmation from them, my own pov is if gauges need fitting then system is heading for replacement anyway.
    Mostly found in the southern part of this green and pleasant land.

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Maintence of hermetic compressors

    Hi All.
    It may or may not eventually transpire that "we" can fit gauges to a R22 system.

    But the rules have now changed and when do they become fact?

    Irrespective of the system years and years this R22 phase-out has been progressing.

    Trying to prolong the inevitable does no-one any good.

    Yes keeping a perfectly good working system makes sense short term.
    But being practical when do "You" draw the line? There are some very good large R22 systems still operational. But they are a ticking financial time bomb all the same!
    And Yes some on here will bend the rules to suit their argument me included, especially when I did not agree in the first place with the end result.
    It is difficult not to try and keep things going for customers, but sometimes we all have to Wake up and Smell the Roses!
    Harry has a real dilemma a warranty can be offered on up to-date and compliant equipment but an aged R22 system?
    Maybe that's your get out clause Harry?
    Grizzly

  15. #15
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Maintence of hermetic compressors

    Quote Originally Posted by hookster View Post
    Regulations do not prohibit the use of R22 equipment even after the deadline. I would actually argue that still using gauges etc to document operating conditions is less detrimental to the environment than waiting for the complete system leakage to occur.


    You can try arguing with the judge but as the law stands:

    From 1st January 2015 it will be illegal to use any HCFCs to service RAC equipment– so recycled or reclaimed HCFC may no longer be used. See Section 5 below formore details.The ban on the use of virgin HCFC gases represents a very real business threat to anycompany which uses refrigerants like R22 or R408A in their processes or air conditioningsystems. R22 remains one of the most commonly used refrigerants in the UK so manyorganisations are going to be affected by the ban. Sectors at greatest risk include the foodand drink industry, petro-chemicals, pharmaceuticals, health, retail, hospitality, finance anddata-processing. Typical applications can vary widely, but examples include refrigerationsystems in supermarkets, blast chillers, cold stores and process coolers and many typesof building air-conditioning as well as in transport refrigeration. Many of these applicationsare absolutely critical to the continued operation of their owner’s business.It should be noted that the bans described above refer to the “use” of HCFCs. In terms ofconsidering what action needs to be taken it should be noted that ‘use’ in relation toequipment containing HCFCs means -

    “the utilisation of controlled substances in the production or maintenance, in particular
    refilling, of products or equipment’’
    This means that it is permissible to carry on using equipment that contains HCFCs beyond
    the phase-out dates, but there must be no maintenance or servicing undertaken on the
    equipment that involves breaking into the refrigerant circuits.

    I am slightly surprised service engineers and trade folk are still unaware of the law and how it affects them and their customers.We have been talking about this for years...

    Our 'arry is up for a *charge

    * pun intended
    https://www.gov.uk/government/upload...-phase-out.pdf
    Last edited by r.bartlett; 13-02-2015 at 08:08 AM.

  16. #16
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Maintence of hermetic compressors

    I am slightly surprised service engineers and trade folk are still unaware of the law and how it affects them and their customers.We have been talking about this for years...

    You and Me both RB.
    Thanks for the clarification all the same, not for my benefit because that is the stance "We" are taking within our company.
    However some wish to continue despite the huge amount of time people have known about this Ban.

  17. #17
    Join Date
    Apr 2010
    Location
    Jamaica
    Age
    34
    Posts
    121
    Rep Power
    16

    Re: Maintence of hermetic compressors

    I know this isn't easy, but it might be helpful to keep in mind: I would recommend analyzing systems extra carefully and if they look worn, I would tell customers before leaving so they won't automatically blame you.
    Visit http://www.kompulsa.com/ for technology news, reviews, and more. Twitter: Kompulsa.

  18. #18
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Maintence of hermetic compressors

    Digressing slightly.

    Two years ago I condemned a williams cabinet with a remote/external condensor that was at least 23 years old, because most of the charge had leaked out and the compressor although still running was like an oven. I also noticed that the cap had been removed and had been recently converted to an XV slightly frosting and a reciever fitted on the condensor unit.

    I made the owner of the kit aware that it still contained R12 as a refrigerant which had not been in use for some years now, and was certainly beyond economical repair and function and idealy needed replacing with new.

    I priced to fully decommission it and have it scrapped, but they never got back to me.

    Guess what... they phoned me on Christmas eve to ask me to come and service it as it wasn't cooling and they couldn't get in touch with the firm that have been out to repair it about several times over the past 2 years!
    Training may be finished but experience is never complete.

  19. #19
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Maintence of hermetic compressors

    to clarify then - if i had a r22 system thats been degassed years ago and recharged with isceon 59 then its ok to stick gauges on it .

  20. #20
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Maintence of hermetic compressors

    But I thought 59 had gone the same route?
    Grizzly

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Maintence of hermetic compressors

    isceon 59 (r417a) is hfc not hcfc!-my theory is "im in the clear your honor"
    Last edited by install monkey; 02-03-2015 at 10:42 PM. Reason: watch rb dig out something thats gonna get me 10yrs! haha

  22. #22
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Maintence of hermetic compressors

    Quote Originally Posted by install monkey View Post
    to clarify then - if i had a r22 system thats been degassed years ago and recharged with isceon 59 then its ok to stick gauges on it .
    Yeah, its ok, its now a R59 system.
    Mostly found in Oxfordshire, UK :)

  23. #23
    Join Date
    Jan 2011
    Location
    england
    Posts
    57
    Rep Power
    15

    Re: Maintence of hermetic compressors

    opened up a can of worms here