    Milky refrigerant



    Hi,
    we do have 2 heat pumps, installed, working fine. But looking to the eyeglasses, on both sides high/low (pictures attached), the refrigerant looks milky ... not clear.
    ( R22 )

    any advice wellcome
    Thank u
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Milky refrigerant

    Hi.
    Call a non European refrigeration Engineer.
    Basic stuff this, which makes me question what YOU do for a living, and being R22.
    Further compounds that question.
    Grizzly

  3. #3
    Join Date
    Oct 2007
    Location
    sweden
    Posts
    93
    Rep Power
    20

    Re: Milky refrigerant

    Humidity indicator button in middle of sightglass shows magenta and magenta on label on sightglass shows Caution - ie you have lot of water/humidify long way over 200 ppm circulating in system and this is not good at all....

    I surprise equipment still working ie seem in very bad condition inside...

    System need checking why humidity coming in inside system (if system is water cooler, is good guess you have leak in evaporator for cooling water), empty out refrigerant (for destruct), repair leak, vacuum in possible days, replace drierfilter _after_ some days vacuum pumping (or new driefilter going to saturate immediately depend of very high water content in system) vacuum again to low steady level, leak check before filling new refrigerant.

    If in Europa - you cannot fill with R22 again and need convert system or using drop in refrigerant for R22 with lower efficient and capacity.
    Last edited by xxargs; 11-02-2015 at 06:53 AM.

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Milky refrigerant

    Quote Originally Posted by housedoctor View Post
    Hi,
    we do have 2 heat pumps, installed, working fine. But looking to the eyeglasses, on both sides high/low (pictures attached), the refrigerant looks milky ... not clear.
    ( R22 )

    any advice wellcome
    Thank u
    Heavily contaminated with Moisture. It's a serious problem that WILL sooner, rather than later be responsible for an expensive repair bill.

    Refrigeration basics 101. No moisture allowed in any refrigeration or A/C systems.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Milky refrigerant

    housedoctor. I believe you could learn from a series of Utube video's posted by one of our respected forum contributors.

    Here's a leg up to his video's.... https://www.youtube.com/user/heavydiesel
    Last edited by mikeref; 11-02-2015 at 08:59 AM.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Dec 2011
    Location
    romania
    Posts
    6
    Rep Power
    0

    Re: Milky refrigerant

    Thank you for the feedback, I try to add also some movies

  7. #7
    Join Date
    Dec 2011
    Location
    romania
    Posts
    6
    Rep Power
    0

    Re: Milky refrigerant

    https://vimeo.com/119413991

    looks like oily ...

  8. #8
    Join Date
    Dec 2011
    Location
    romania
    Posts
    6
    Rep Power
    0

    Re: Milky refrigerant


  9. #9
    Join Date
    Dec 2011
    Location
    romania
    Posts
    6
    Rep Power
    0

    Re: Milky refrigerant