Thread: Calorex heatpump
-
12-05-2008, 07:36 PM #1
Calorex heatpump
Hi guys, I've got a calorex heatpump dating from 89' and its on R502. The compressor is duff and i've been advised by calorex that a R407C compressor along with a new TEV will get it up and running again.
They have advised running the system on R407C but i would think that R22 would be better considering the old system ran with mineral oil and R502.
Opinions please
Cheers Jon
-
12-05-2008, 08:35 PM #2
Re: Calorex heatpump
-
12-05-2008, 08:44 PM #3
Re: Calorex heatpump
Bite the bullet and flush the sytem, change oil type....how about R507 instead of R407c....much closer to R502.
-
12-05-2008, 10:14 PM #4
Re: Calorex heatpump
Why don't you just replace the unit?
In the long run, surely this would be more beneficial!
Cheers
Jase
-
12-05-2008, 10:50 PM #5
Re: Calorex heatpump
Why hasn't it been ripped out and been replaced before?
I bet its not on its original compressor.
I've never seen one run on R502 every old one I have ever been involved with were all R22.
If I were you, and if you couldn't replace the entire unit, I would put a R22 comp and valve in it, while you still can.
Andy
-
12-05-2008, 10:58 PM #6
Re: Calorex heatpump
Anything but R 407c. I would have put in R22 or R404A/507.
-
12-05-2008, 11:32 PM #7
Re: Calorex heatpump
Thanks for the replies
I think i will price for a new heatpump tommorrow, but i think calorex will only supply these through thier dealers and i'm not one of them
Its definatly on R502 as it has a blue R502 sticker on the comp. and it also says the same on the model info sticker R502 3.85kg
I don't much like R407C either, though i think this is what all the new ones run on.
Also i was thinking of the F gas inspection requirement if i fill this with R407C as these things use automotive style reciever/driers and unless i can get a braze in one as opposed to flared, the customer will have to it inspected etc every year.
Cheers Jon
-
23-06-2008, 08:20 PM #8
Re: Calorex heatpump
Why don't you use R408 drop in for R502
-
23-06-2008, 10:49 PM #9
Re: Calorex heatpump
Hi Jsimon,
I'm stuck with buying the compressor from the manufacturers as the model plate has rusted away on the old one and hence have no idea what it was to get an equivalent R404A one that i could run on R408A or similar.
Its got a new R407C comp on it now and i'm running it on R22 due to concerns about residual mineral oil content of the system. This is causing a little bit of fun in getting the superheat correct, but thats another story....
Cheers Jon
-
25-08-2008, 03:14 PM #10
Re: Calorex heatpump
Hi Jon
A bit late to help you this time, but with over 20 years working on Calorex systems you were right about the 502 they used to use it in all their heat pumps.I have used 22 in all the old 502 systems for years and have had no problems.
-
29-08-2008, 06:15 PM #11
Re: Calorex heatpump
Cheers Chizel010,
Systems been running on R22 for a couple of months now with no problems.
Cheers Jon
Similar Threads
-
Heatpump for water & Space heating?
By gdidi in forum Technical SpeculationsReplies: 3Last Post: 13-09-2007, 09:28 AM -
High overcurrent on 3.5kW heatpump split
By Makeit go Right in forum Air ConditioningReplies: 12Last Post: 08-03-2007, 12:27 AM -
heatpump blowermotor
By Kfoam in forum Trouble ShootingReplies: 2Last Post: 28-01-2003, 09:18 PM -
Heatpump up to 100°C
By Moeller in forum New TechnologiesReplies: 1Last Post: 13-10-2002, 11:13 PM