    Feb 2010
    Bulgaria
    Climaveneta Heat pump - Carel alarm
    Can anybody help me solve problem with alarm for Climaveneta heat pump ?
    The model is Climaveneta / MICS-N 0152 - 40 KW
    The machine use controller - Carel Microchiller 2 and when i run it it show alarm A1 (low ambient temperature)
    I set up Antifreeze set point to -10 degree and but again it happen
    The machine use electronic expansion valve Carel
    manchester
    5,639
    Re: Climaveneta Heat pump - Carel alarm
    http://www.novatherm.de/f5-edit/ups/...E%20Bedien.pdf
    A1 freeze protect, check pumps,strainer, system has water/glycol in, turn it off and test resistance on sensors to see if theyre all reading similar resistances at ambient temp
Tags for this Thread