    Refrigerant velocity limitation in evaporator ?



    Hello, I have found that,in suction line refrigerant velocity must be higher than 8-10 m/s for proper oil return.
    I wonder about is there any highest velocity limitation value for the evaporator inlet ? for refrigerant R744



  2. #2
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Refrigerant velocity limitation in evaporator ?

    Oil return in a (dry?) riser very dependent on viscosity and temperature....and in the case of 744, the means and flows associated with defrosting, where applicable.

    As to inlet side: effective distribution says there is a lowest velocity for a flashing refrigerant feeding multiple cap tubes; with velocity increasing, material erosion is the next effect of consequence; and neglecting very low temperature and pressure effects, the next portion of the envelope is established at high velocities associated with near-sonic 2-phase flows. Doubt you will be working near that last limitation.

  3. #3
    Join Date
    Feb 2015
    Location
    TURKEY
    Age
    35
    Posts
    2
    Rep Power
    0

    Re: Refrigerant velocity limitation in evaporator ?

    Thank you sterl