    R407F LT pack problem



    Has anyone worked ona space pack running r407f LT?
    I got some glass door freezers struggling to run to temp and they alarm every couple of days, i heared the 407f is not a good gas to be used for LT.
    The suction pressure is 0.9/1bar and discharge is 13bar.
    Last edited by Gaz22; 05-02-2015 at 05:39 PM.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R407F LT pack problem

    Quote Originally Posted by Gaz22 View Post
    Has anyone worked ona space pack running r407f LT?
    I got some glass door freezers struggling to run to temp and they alarm every couple of days, i heared the 407f is not a good gas to be used for LT.
    The suction pressure is 0.9/1bar and discharge is 3bar.
    Are they discharging to HT compressors (compound) or is that a typo?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: R407F LT pack problem

    Hi Gaz
    I hope that discharge pressure is 13Bar not 3 Bar?.
    What expansion valves are fitted and what are the superheats on these cabinets ?.

  4. #4
    Join Date
    Nov 2009
    Location
    UK
    Posts
    40
    Rep Power
    0

    Re: R407F LT pack problem

    check the glide setting in the case controllers

  5. #5
    Join Date
    Jan 2009
    Location
    UK
    Age
    58
    Posts
    161
    Rep Power
    16

    Re: R407F LT pack problem

    0.9/1bar is not low enough for LT cabinet operation you need at least -35C evaporating condition for FGD cabinets!
    Mostly found nowadays at the sharp end of the stick!

  6. #6
    Join Date
    Nov 2014
    Location
    London
    Age
    41
    Posts
    13
    Rep Power
    0

    Re: R407F LT pack problem

    Quote Originally Posted by Rob White View Post
    Are they discharging to HT compressors (compound) or is that a typo?

    Rob

    .
    Hi yes its a dual temp pack

  7. #7
    Join Date
    Nov 2014
    Location
    London
    Age
    41
    Posts
    13
    Rep Power
    0

    Re: R407F LT pack problem

    Quote Originally Posted by Glenn Moore View Post
    Hi Gaz
    I hope that discharge pressure is 13Bar not 3 Bar?.
    What expansion valves are fitted and what are the superheats on these cabinets ?.
    The suction is 1 bar, the discharge is 11 bar.

    Its a carter glass door freezer 3 freezers next to each other with only a plastic divider between them and 3 doors on each freezer.
    They are fitted with thermostatic expansion valve and super heat is 4.2 for first freezer, 6.4 for second one and 6.5 for third one. At the time those reading were taking, none of the freezers had any alarms. But super heat on the 3rd cabinet gets to 8/11 and temp goes down to -15 when it alarms
    The first one never alarmed since install over 2 years ago.
    Last edited by Gaz22; 05-02-2015 at 05:43 PM.

  8. #8
    Join Date
    Nov 2014
    Location
    London
    Age
    41
    Posts
    13
    Rep Power
    0

    Re: R407F LT pack problem

    Quote Originally Posted by Silhouette View Post
    0.9/1bar is not low enough for LT cabinet operation you need at least -35C evaporating condition for FGD cabinets!
    I know but when the pack is setted to lower pressure it keeps tripping on lp on a cold day so they raised it up.
    Last edited by Gaz22; 05-02-2015 at 05:43 PM.

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R407F LT pack problem

    .

    Higher superheat means less liquid in the evaporator (for whatever reason).
    If the evaporator is being starved for any reason then that might cause this.

    If it is cutting out on LP in the cold weather and if you need the systems
    to run lower than it is, somebody needs to correctly commission the whole
    pack and set it up as it should be.

    Sometimes on packs if there is an issue with liquid distribution then individual
    cases suffer and it tends to be the same cases. You need to establish
    when the cases alarm and what is happening on the pack when that happens.

    Just adjusting a control to stop an issue is not the real answer and can lead
    to other problems.

    Rob

    .
    Last edited by Rob White; 06-02-2015 at 10:35 AM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  10. #10
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R407F LT pack problem

    .

    Have you ever had any leaks on the system in the 2 years that
    you say it ran ok without any alarms? 407 fractures if it
    leaks and the results can be very confusing if you have never
    encountered it before. Weird pressures and abnormally low suction
    pressures compared to new virgin refrigerant.

    R407f is blended R32, R125 and R134a.

    The 134a tends to leak out first and you are basically left with R410a.

    Has this pack ever lost refrigerant over the last 2 years?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  11. #11
    Join Date
    Jun 2001
    Location
    Gloucestershire
    Posts
    13
    Rep Power
    0

    Re: R407F LT pack problem

    The 134a does not separate out from the other two components. Depending on where a leak occurs, the three components may leak out in different proportions from the original composition. It is usual that the higher pressure components leak in a greater percentage. This would make 407 blends richer in 134a by a few percent and you could expect to see a small loss of capacity. Topping up usually restores the blend back to specification. At lower temperatures it is more important that glide is taken into account when setting the TXV.

  12. #12
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: R407F LT pack problem

    Are the expansion valves made for R407F or is this a retrofit job using R22,R404a, or R407c expansion valves, if the valves are not specifically made for R407F then the valves will never function correctly due to their Static Superheat curve will increase the Superheat control of the valve, the lower you go in evaporator temperature .