Gravity condensate size on 10kw cassette.....
Hi All,
Am looking to clarify if it's ok to fit 1' 1/4" condensate connected to the standard drain attachment that comes with a Daikin cassette?
The drain will initially be fitted vertical as usual as aware that the cassettes have an internal pump fitted.
I usually abandon the attachment and fit a rubber adaptor (Pump House or Sauermann) that downsizes to 3/4" overflow without a problem but never gone straight to 1' 1/4" off the cassette. Have looked in the manual for recommended condensate pipe size but could not find anything.
Any advice or previous experiences from this would be much appreciated
Thanks
-
31-01-2015, 01:46 PM #2
Re: Gravity condensate size on 10kw cassette.....
Can't see a problem with running it in 1 1/4" i think for fujitsu that is the recommended size anyway, though often it is reduced for cheapness and easyness of installation.
Mostly found in Oxfordshire, UK :)
-
31-01-2015, 01:58 PM #3
Re: Gravity condensate size on 10kw cassette.....
The only possible problem is when the internal pump stops, the amount of water that back-flows into the cassette from the initial vertical section might be sufficient to cause an overflow of the drip tray if you use 1-1/4", however this is much less likely if the vertical is 3/4".
Mobile A/C at its best, see avatar.
Bedford. Now retired and trying to relax.
-
31-01-2015, 03:57 PM #4
Re: Gravity condensate size on 10kw cassette.....
on 3/4 overflow a daikin lift pump will do 760mm- calculate the volume of 3/4 overflow and compare it to 1 1/4 and that will give you your max lift - best case is to use the flexi to send the drain up and stick a 90 bend on itand ensure you get the fall of 1cm per mtr