    Gravity condensate size on 10kw cassette.....



    Hi All,

    Am looking to clarify if it's ok to fit 1' 1/4" condensate connected to the standard drain attachment that comes with a Daikin cassette?

    The drain will initially be fitted vertical as usual as aware that the cassettes have an internal pump fitted.

    I usually abandon the attachment and fit a rubber adaptor (Pump House or Sauermann) that downsizes to 3/4" overflow without a problem but never gone straight to 1' 1/4" off the cassette. Have looked in the manual for recommended condensate pipe size but could not find anything.

    Any advice or previous experiences from this would be much appreciated

    Thanks



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Gravity condensate size on 10kw cassette.....

    Can't see a problem with running it in 1 1/4" i think for fujitsu that is the recommended size anyway, though often it is reduced for cheapness and easyness of installation.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Gravity condensate size on 10kw cassette.....

    The only possible problem is when the internal pump stops, the amount of water that back-flows into the cassette from the initial vertical section might be sufficient to cause an overflow of the drip tray if you use 1-1/4", however this is much less likely if the vertical is 3/4".
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Gravity condensate size on 10kw cassette.....

    on 3/4 overflow a daikin lift pump will do 760mm- calculate the volume of 3/4 overflow and compare it to 1 1/4 and that will give you your max lift - best case is to use the flexi to send the drain up and stick a 90 bend on itand ensure you get the fall of 1cm per mtr