    Jan 2010
    India
    35
    3
    McQuay Chiller Problem
    HI,
    I have a mcquay chiller PFS 330.3 ( china ) with Siemens controller.
    It does not show any alarm but still the compressors are not taking the start command.
    the startup time is set at 180 sec and the countdown is not starting.Kindly help
    May 2010
    Greece
    42
    Hi first of all check the evaporators water flow, clean strainer, make sure pump works properly or the flow switch!! If you don't have enough Δp the machine will not start.
    Apr 2011
    Russia
    139
    Re: McQuay Chiller Problem
    Did you check remote on-off contact?
    Jan 2010
    India
    35
    3
    Thanks guys.It was the flow switch issue.
    Jan 2010
    India
    35
    3
    McQuay Chiller Date issue
    I have a McQuay PFS 330.3 . Date is not getting updated in the chiller controller.
    I am using the admin login but still no success. Please suggest.