    McQuay Chiller Problem



    HI,

    I have a mcquay chiller PFS 330.3 ( china ) with Siemens controller.
    It does not show any alarm but still the compressors are not taking the start command.
    the startup time is set at 180 sec and the countdown is not starting.Kindly help



  2. #2
    Join Date
    May 2010
    Location
    Greece
    Age
    42
    Posts
    16
    Rep Power
    0
    Hi first of all check the evaporators water flow, clean strainer, make sure pump works properly or the flow switch!! If you don't have enough Δp the machine will not start.

  3. #3
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    15

    Re: McQuay Chiller Problem

    Did you check remote on-off contact?

  4. #4
    Join Date
    Jan 2010
    Location
    India
    Age
    35
    Posts
    3
    Rep Power
    0

    Re: McQuay Chiller Problem

    Thanks guys.It was the flow switch issue.

  5. #5
    Join Date
    Jan 2010
    Location
    India
    Age
    35
    Posts
    3
    Rep Power
    0

    McQuay Chiller Date issue

    Hi,

    I have a McQuay PFS 330.3 . Date is not getting updated in the chiller controller.
    I am using the admin login but still no success. Please suggest.