    bitzer screw compressor



    i have a Bitzer HSN7471 screw compressor that is bursting the piping on the oil cooler of the system. has anyone ever had this before? there three systems on the site but only one is bursting.
    i can not see anything obvious that would cause this.
    any help with this would be appreciated.:confused



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: bitzer screw compressor

    what you mean of bursting ?
    what type you used for oil cooling.

  3. #3
    Join Date
    Jan 2015
    Location
    SOUTH AFRICA
    Posts
    5
    Rep Power
    0

    Re: bitzer screw compressor

    hi there
    the actual pipework from the oil separator to the air cooled oil cooler is bursting, it starts by bulging and eventually splits down one side of the pipework. the oil we are using is BH170 and the temperature of the oil line where it goes into the sump of the screw compressor is 63-65 degrees Celsius. there is a check valve on the oil line which is functioning correctly as well as the flow switch and solenoid valve. the overall temperatures on the affected screw are all lower than the other screws which are all functioning correctly and do not burst.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: bitzer screw compressor

    Check valve, seems unusual, what's it's purpose?
    If oil/refrigerant locked between solenoid & check valve expect possibility of exceptionally high pressures
    whatever check valve is for I'm not sure, but it should be after solenoid, not before, if that's the case.
    Oil cooler should also have a relief valve to protect it as well against over pressure.

  5. #5
    Join Date
    Jan 2015
    Location
    SOUTH AFRICA
    Posts
    5
    Rep Power
    0

    Re: bitzer screw compressor

    Quote Originally Posted by RANGER1 View Post
    Check valve, seems unusual, what's it's purpose?
    If oil/refrigerant locked between solenoid & check valve expect possibility of exceptionally high pressures
    whatever check valve is for I'm not sure, but it should be after solenoid, not before, if that's the case.
    Oil cooler should also have a relief valve to protect it as well against over pressure.
    thanks
    we have already started to reposition the solenoid valve to see if this will cure the problem.

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: bitzer screw compressor

    I did a lots work with Bitzer screw compressor as same as HSN & HSK with different types
    Water cold and air cold also with ECO.
    in oil line you should not have loop.
    you should have from oil separator
    1) valve
    2)oil cooler
    3)valve
    4) oil filter
    5)solenoid valve
    6) flow switch
    7) sight glass
    8) valve
    compressor
    it is better you put 2 gags in inlet and outlet of filter
    and also 3 way oil valve is by pass oil when it is cold

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: bitzer screw compressor

    Quote Originally Posted by zacool View Post
    thanks
    we have already started to reposition the solenoid valve to see if this will cure the problem.
    Zacool,
    Can you advise us on position of all the components in oil line?
    If you re-position solenoid maybe something else happens, especially with this mystery check valve.
    Also refrigerant. what type of tube you are using & it's pressure rating.

  8. #8
    Join Date
    Jan 2015
    Location
    SOUTH AFRICA
    Posts
    5
    Rep Power
    0

    Re: bitzer screw compressor

    the components are as follows: oil separator,valve, check valve, filter, flow switch, solenoid.
    the tubing used is from a major local manufacturer by the name of Maksel and we are using tubing rated for R410a. so tubing is not issue. this is specific to the one screw compressor condenser. the other compressor packs are fine. it must be something specific with the particular pack.

  9. #9
    Join Date
    Jan 2015
    Location
    SOUTH AFRICA
    Posts
    5
    Rep Power
    0

    Re: bitzer screw compressor

    I forgot to add the sight glass which is after the solenoid.

  10. #10
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: bitzer screw compressor

    you did wrong pipes works
    if you see the bitzer documents there is no check valve in pipe line and also where is the position of oil cooler?
    1) valve
    2)oil cooler
    3)valve
    4) oil filter
    5)solenoid valve
    6) flow switch
    7) sight glass
    8) valve
    compressor

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: bitzer screw compressor

    The compressor discharge valve is a stop check as well, there will be a check valve on outlet of oil separator and a solenoid on oil feed into compressor. If oil cooler tubes are swelling and bursting then oil is trapped and hydraulicing the tubes, suggest the oil temp regulation 3 way valve (AMOT ) is installed incorrectly or jammed or faulty, as oil temp is too low entering compressor.
    just a thought, magoo