    Fitting a Ranco K59 Thermostat



    Hi Guys

    I am replacing a Thermostat on my Old Electrolux F/F , the Capillary tube goes from the Thermostat then inside a plastic sleeve about 40cm long along the top of the F/F ( Attached pic ) inside the sleeve there is a cable that is a loop , it comes from junction box ( compressor ) then loops around the inside of the sleeve then back down again , the Question is what is the cable looping for ! .


    cheers

    spike
    Attached Images Attached Images
    Last edited by spike47; 26-01-2015 at 11:56 AM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fitting a Ranco K59 Thermostat

    prevent condensation running down cable and shorting at the connections at a guess

  3. #3
    Join Date
    Jan 2015
    Location
    England
    Age
    57
    Posts
    3
    Rep Power
    0

    Re: Fitting a Ranco K59 Thermostat

    Thanks for your reply , can there be any condensation in that area ! ,everything is outside the Fridge , no refrigerant in that area .

    cheers

    spike

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fitting a Ranco K59 Thermostat

    cold air from inside the cabinet -the sleeve goes to outside the cabinet, dunno, i avoid domestics like ebola

  5. #5
    Join Date
    Jan 2015
    Location
    England
    Age
    57
    Posts
    3
    Rep Power
    0

    Re: Fitting a Ranco K59 Thermostat

    Hi

    Thanks again for your reply , the sleeve only lays on the top of the Unit about its about 35/40cm long , does not go inside .

    thanks again

    spike

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Fitting a Ranco K59 Thermostat

    UK Fridges are obviously beyond my knowledge. I'd do a resistance test on the extra wires.

    Chances are....it's an off cycle defrost assisted heater. The reason for this is to have a Mechanical Thermostat restart your compressor shortly after the ice is gone.

    Domestic fridges in Northern Australia have no need for these accessories.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Fitting a Ranco K59 Thermostat

    .

    You say it is a fridge / freezer?

    The stat is outside the fridge completely and the phial goes into the fridge?
    The sleeve has this looped white cable, is it a heater cable? Because if it it
    and if it is a fridge freezer could it be used to assist in the switching on of the thing?

    Is the thing an "environmentally" controlled one? By that does it have a label on
    the back saying it will work in a colder ambient?

    And finally what refrigerant is it on, Care 30, Care 40 maybe (propane/butane mix or propane)?

    Lots of questions but some fridge freezers suffer in low ambient conditions
    and to get around it they sometimes put little trace heaters inside to warm
    the thing up. Traditional fridge / freezers using one stat only control the
    fridge temperature and if the fridge is correct then the freezer is also. That
    meant in low ambient conditions the fridge did not rise enough in temperature
    to get to the cut in point (in a garage or outhouse) and if the fridge did not
    get warm enough to cut in then the freezer stood at + temperatures and thawed
    out.

    The normal cut in temp was about +7 degC and it was fixed so the fridge manufactures
    started putting small low wattage trace heaters that sometimes were wired through the
    compressor winding's, when the fridge turned off the heater came on and slowly warmed
    up the fridge to the cut in temperature.

    Now with modern Care (flammable) refrigerants they have moved all switches (including stats)
    out of the fridge and therefore they maybe more susceptible to ambient temperatures
    so they put a little trace heater in with the phial to compensate.

    I might be completely wrong though

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    Jan 2015
    Location
    Yorkshire
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: Fitting a Ranco K59 Thermostat

    Hi Rob

    Thanks for your feedback , you are correct in your satement , it does indeed have a trace heater that energises when the comp goes off .

    cheers

    spike