    Cool 2 companies, 2 techs still having issue



    These repairs are with in a month.
    The first due to my outside unit on my heat pump 2.5 tons, 13 years old, making noise and freezing. He replaced the motor two days later same noise. When I called them back out they said the fan was making the noise. They would order it, a week and half later, I am at warehouse picking up fan myself. They said the freezing was normal.

    Not willing to call back first tech that would not pick up phone when I called an yes this was a company.
    I started trouble shooting
    Still freezing I check the defrost board and it going into defrost by jumping the pins.

    Second tech an inch of ice on outside unit. 2.5 lbs *****, the temp on the line went from 117 to 150, he raise the defrost time to 80 from 60 seconds. He said the fan was running in defrost. He was not sure why this would happen.

    The unit is still frosting heavy this morning with ice on Cage, lucky it melted due to warm temp.
    Would the ICP Heat Pump Contactor cause the fan to stay on and reduce the efficiency of the defrost mode. What else could cause fan not turning off and freezing.

    Two company two techs



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 2 companies, 2 techs still having issue

    We don't get that style of unit here so i am not familiar with it, but, i believe the fan power supply is fed through the defrost board so if the fan is staying on when it should not it is likely the board is faulty. Though you would need to test it while it is working and then defrosting to see what is going on.
    It may also be possible that the fan was wired in differently when it was changed and now no long is connected through the defrost board.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: 2 companies, 2 techs still having issue

    Hmmm,

    As Mr. Spanners states above, not familiar with that unit here on this side of the pond.

    However,
    13 year old unit that need work on it that the first engineer couldn't fix?
    Sure it wouldn't be more financial viable to let the unit retire to the great junkyard in the sky?

    A new unit would have much higher efficiency (= run cheaper), come with a warranty and most likely not cost a lot more than what the bill for the repairs of your existing unit are likely to be.