    cap-tube !



    If the capillary tube was to long, Does this affect the temperature?
    I am working on cycle using gas R404a and I want to get to -30 c ,
    The length of the capillary tube 3 meters (48) and the maximum temperature reached it is -15 c
    The pressure of the gas in the suction line 2.2 bar (30.2) psi
    In your opinion, what is the problem?



  2. #2
    Join Date
    Dec 2006
    Location
    UK
    Posts
    106
    Rep Power
    19

    Re: cap-tube !

    2.2 Bar is way too high, but we need a more information really to help you out; such as the orifice size of the cap, the high side pressure, more info about the appliance etc.

    However, for very low temp refrigeration such as -30, I wouldn't recommend capillary. You say that you are “working on cycle using gas R404a and I want to get to -30 c”; was the system designed to work at these temps, or are you building the system yourself (if you are consider a system using a TEV).

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: cap-tube !

    The way to size capillary tubes is not by temperature or pressure.

    Get your superheat right and the rest will follow. (Longer cap tube = higher super heat, shorter = lower)


  4. #4
    Join Date
    Sep 2014
    Location
    israel
    Age
    34
    Posts
    17
    Rep Power
    0

    Re: cap-tube !

    yes i build the system by my self , the cap-tube is (0.048 " Diameter ) i cut a 50 cm from the cap-tube , now its a 2.5 m , the low side pressure is 3 bar and the high side 7 bar , the temperature is -5 !!
    and thank you for replay

  5. #5
    Join Date
    Sep 2014
    Location
    israel
    Age
    34
    Posts
    17
    Rep Power
    0

    Re: cap-tube !

    " The way to size capillary tubes is not by temperature or pressure.

    Get your superheat right and the rest will follow. (Longer cap tube = higher super heat, shorter = lower) "
    i didnot understand
    could you please speak in details

  6. #6
    Join Date
    Oct 2007
    Location
    sweden
    Posts
    93
    Rep Power
    20

    Re: cap-tube !

    Measure temperature short after end off capillary tube in evaporator and measure temperature on suction pipe outlet short after evaporator (few cm) and temperature differences between points calls superheat - if 3-5 degree C fine.

    If almost zero, you possible flooding compressor with liquid refrigerant, > 5-6 degree C, evaporator starving of liquid refrigerant.

    if you have OK Superheat but still to warm in box - check air circulation inside box, check if insulation on box or put in bigger machine and evaporator.

    if you can download data-sheet on your compressor - you can see cooling capacity in different temperatures on evaporator side and assume evaporator temperature at least 5-10 degree lower than air temperature in yor box under running if not using active air circulation trough evaporators surface inside box.

    most classic refrigerator have around -10 degree C on evaporator under compressor running to hold temperature around +2 - +5 degree C in box.
    Last edited by xxargs; 18-01-2015 at 06:50 AM.

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: cap-tube !

    One has to select a Capillary tube's internal diameter and the length of that tube by the compressor displacement...temperature required, and refrigerant used on your kit. There are charts out there for Cap tube selection.