15-01-2015, 10:19 AM #1
Compressor selection for blast freezer
Dear All,
I need suggetion to identify an 2stage reciprocating compressor(R717)for my existing blast freezer.
Room size is 7meters long 4.5meters wide and 3meters height build with 180mm insulated panels.
Exisisting compressor was Frick Tdsh 163s with 132kw motor.
Shell and tube condenser with Bac cooling tower.
Liquid vessel with Witt GP-40 Hermatic liquid pump.
Evaporator with Woods Heatproof/Aerofoil type 2 x 7kw/1475rpm/960mm diameter Unknown model.
Size of the evaporator is 380cm long x 150cm wide x 215cm height, 1inch pipe with 12 vertical rows and 24 harizontal rows.
Reason for replacement: Due to high electricity consumption and poor performense 1996 model package.
15-01-2015, 03:26 PM #2
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Compressor selection for blast freezer
To advise you need to Know?
1)load tons in Room
2)Room temp.
3) why you want to use reciprocating compressor why not screw compressor ?
Any way if you want to use all your equipment you have ( condenser - evaporator ) , you have to use same capacity of compressor is there .
you could use sabro- mycom- or other brands .
how you find it , did you compare with new system
did you checked your system and tried to improve your system
22-01-2015, 08:38 AM #3
1, 705 m2 surface area of the evaporaotr as per the supplier specification.
Size of the evaporator is 380cm long x 150cm wide x 215cm height, 1inch pipe with 12 vertical rows and 24 harizontal rows. 15ton capacity approx?
2, Room temperature is -25c.
3, This system was reconditioned/overhauled in 1994.
Planning to use exisiting Shell and tube condenser,Cooling tower,Liquid vessel,evaporator.
Sabroe TSMC 108Swith 55kw motor or Grasso V450T with 45kw motor can be used for this application?
Thanks in advanse for your assistanse.
22-01-2015, 10:30 PM #4
On existing plant replace all electric motors with high efficiency modern motors and save approx. 10>12% power usage, upgrade existing power factor correction system IF installed and save another 10 + % if no PF correction install one.
24-01-2015, 11:33 AM #5
Thanks for the suggestion.