    Helium leak testing



    Guys

    Anyone offer some advice regarding the best leak detector when using helium as a trace element during leak testing?

    We have a large VRV install with a small leak and the original installer has used Armaflex tape on all the refnets and flares, so uncovering them is going to be a nightmare



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Helium leak testing

    unwrap the tape off the flares- indoors come with sleeves - had a mitsi unit to pressure test in nottingham- used 3 bottles of nitro- wouldnt hold 5 bar- had to crank the bottle upto 40 bar to hear the 2 open ends in the ceiling space

  3. #3
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Helium leak testing

    Hi Frank, I use JAVAC http://www.javac.co.uk/gas-mate-hydr...292.html,along with climate centres trace gas, and have never failed to find a leak with it so far. Pressure test system to around 6 bar use as a normal electronic detector. Can be an issue pinpointing large leak as the detector is so sensitive, you can ad just the sensitivity though.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Helium leak testing

    Quote Originally Posted by install monkey View Post
    unwrap the tape off the flares- indoors come with sleeves
    They haven't fitted the flare covers - taped everything up, including the refnets
    We've started stripping and testing the flares but it's taking too long

    - had a mitsi unit to pressure test in nottingham- used 3 bottles of nitro- wouldnt hold 5 bar- had to crank the bottle upto 40 bar to hear the 2 open ends in the ceiling space
    Probably one of my installs then

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Helium leak testing

    Update
    splashed out some cash and bought the Javac 718-202-G1sniffer.
    Found the leak inside one of the cassettes. ...�� using the tracer gas

    Thanks for the heads up

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Helium leak testing

    Frank,

    use this stuff on all your flares and you never have a leak there any more.

    http://www.refrigtech.com/Product/Se...ylog_blue.html

  7. #7
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: Helium leak testing

    Hey Frank did the nitro with the helium make it easier to find the Leak? I was told that the helium has smaller molecules so you use less to find the leaks. Any feed back would be good.
    Thanks

  8. #8
    Join Date
    Oct 2007
    Location
    sweden
    Posts
    93
    Rep Power
    20

    Re: Helium leak testing

    Helium is (very) expensive depend of production in USA scaled down long time and helium in air can make interference in your search ie. ~ 5 ppm Helium in air.

    New solution is using nitrogen with 1% hydrogen and sensors can detect to air level of hydrogen as 0.5 ppm

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Helium leak testing

    Climate centre sell trace gas which is 95% nitrogen and 5% hydrogen.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Helium leak testing

    Thanks Guys

    It was the Tracer gas from FSW together with the Javac sniffer http://www.javac.co.uk/gas-mate-hydr...-pr-16292.html

    Well done CONRAD...good call.

    I thought that it was Helium but it turns out it is Hydrogen/OFN mix.

    Another tool to add to my ever expanding tool chest.

    Chemi
    It wasn't one of my installs...they usually leak like a sieve and the leaks are easy to find

  11. #11
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Helium leak testing

    Glad it worked for you too Frank!!. The comparative high cost of the Tracer gas compared to OFN has to be worth it if it saves labour time.

  12. #12
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Helium leak testing

    Quote Originally Posted by frank View Post
    Update
    splashed out some cash and bought the Javac 718-202-G1sniffer.
    Found the leak inside one of the cassettes. ...�� using the tracer gas

    Thanks for the heads up
    leak inside?

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Helium leak testing

    Quote Originally Posted by r.bartlett View Post
    leak inside?
    Yes... Leaking coil

  14. #14
    Join Date
    Feb 2015
    Location
    melbourne,vic
    Age
    35
    Posts
    2
    Rep Power
    0

    Re: Helium leak testing

    Hi..I am using multiRae pro,a multiple gas detector.It is a portable,hand held detector having PID.I am using it and is working fine for me....

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Helium leak testing

    Any link to the manufacturers Web site?