Results 1 to 6 of 6
  1. #1
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    How to adjust head on a water cooled condenser



    How do you properly adjust the head presure on a water cooled condensing unit? I was told to adjust water flow to produce a head presure equivalent to 105 degrees F (after convertion of presure to temperature) regardless of refrig type. Also, how much does the entering water temperature influence this procedure.

    I have a need to set up a display case for shipping. I will only have tap water, which is approximately 55 degrees F, for the set up. If the location has a cooling tower I'm fairly certain it will be a different temp than my tap.
    Ken
    Last edited by kengineering; 22-04-2006 at 03:49 PM. Reason: additional comments



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: How to adjust head on a water cooled condenser

    Ken,

    Are you using a water regulating valve controlled by discharge pressure?

    The valve setting will be different for cold water, since the required flow rate will be lower.

    If a cooling tower is used, the valve setting will require more water during the summer because of the higher wet bulb temperatures and the effect of this on the outlet water temperature from the tower.

    105F is a nominal design temperature that a lot of people use for some reason. If the system can operate with lower condensing temperature (and most of them can), the water regulating valve can be adjusted further open.

    The final adjustments will have to be done during start-up.

    Was the system designed for 105F condensing, or is this just a number someone is throwing around?

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: How to adjust head on a water cooled condenser

    when we installed WC condensers in a ship, we adjusted the valve to the saturated pressure of the warmest expected seawater + 10 K for the refrigerant used.
    So the water can become max 18°C during summer, so it was set to condens a 28°C.

    If it's a capillary fed system, then you will need to design your system at the highest possible condensing temperature and maintain that pressure very stable.
    So you can use in your case 65°F to 70 °F.
    The lower you condens, the better for the power consumption.

    But if it is fresh water, then you have to make compromises.
    This fresh water costs a lot of money so it flows all to the sewer. The gain you have in power consumption is lost in water consumption.

    In such a case, I should let in condens on the same pressure a normal installation should condens when it was aircooled.

    Install also a SV in case the pressure regulating valve should leak.
    if it leaks for weeks, the then you have spoiled a lot of fresh water.

    Ever wondered that 1 l of fresh water in bottles costs almost the same of 1 l. fuel?? And think once at the almost uncountable handling's, transports, refining, ... there has to be done to make 1 l. of fuel!
    You can plot this in a graph: water cost versus power savings and look where lines are crossing.

    You have the same with fans running on a condenser to lower HP and to increase the COP.
    On a certain moment, too many fans will run for the savings you gain on the compressor side.


    PS: IN general for all readers, try to place SI units between brackets. I tend not to read posts with to many IP units.
    And SI posters better place the IP units between brackets.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: How to adjust head on a water cooled condenser

    Danfoss and Jonhson control have modulating pressure valves to adjust the water flow based on condensing pressure.
    Be careful that cold water will cause unexepectedly high subcooling at low flow rates.

  5. #5
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: How to adjust head on a water cooled condenser

    In such a case, I should let in condens on the same pressure a normal installation should condens when it was aircooled.
    Here in the States Copeland data sheets rate condensing units on a chart starting at 90 degrees f (32 c ) and as teperature goes up from there the capacities diminish. So it would seem that would be the place to start. Thanks, Ken

  6. #6
    Join Date
    May 2006
    Location
    Toronto, Ontario,
    Age
    59
    Posts
    8
    Rep Power
    0

    Re: How to adjust head on a water cooled condenser

    Not that simple.

    As a general rule of thumb, we use a condensing temp of 90 to 100F. The lower your cond temp the greater your subcooling and therefore the higher the efficiency and capacity. To correctly charge the system however becomes more tricky. I will assume AC conditions. Ensure you have a full load - no unloading. First charge the system with the minimum charge (or add refrigerant while the unit is running). Adjust the head pressure control until you get 210 to 250 psi (R22). Continue to add gas until your discharge superheat reaches 75F or less. Do not go lower that 60F (overcharge). If you lower your head pressure too much, you will not have good oil return.

    Hope this helps

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 01:25 PM
  2. water cooled condenser shell type
    By abbasi in forum New Technologies
    Replies: 0
    Last Post: 27-04-2005, 08:32 AM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. water cooled condensers
    By aaron crimmins in forum Fundamentals
    Replies: 2
    Last Post: 22-07-2002, 04:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •