    Question Vector 1850 overload code



    Have a vector that seems to bring up
    An overload code every now and then.
    Have checked for 12v on HC19 and 2MP26
    As stated in help book and checked
    Nothing going to ground.
    Passes a pretrip no dramas.

    Anyone else experienced this?

    Apologies for all the vector questions,
    Recently have been given a heap to look
    After. Worked for a TK dealer for ten years
    And only recently getting solid time on Carrier
    Any TK questions fire away



  2. #2
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: Vector 1850 overload code

    what exactly is overloading ? If it passes a pretrip, it might be related to the ambient and conditions.
    Is the condenser clean ? Enough gas ?
    Is there sufficient space under the fridge for the air to get out ? (for our european viewers, the 1850 is commonly used on the lead trailer of a multi combination, commonly with a fuel tank sitting very close underneath it)
    And lastly is the truck pulling it close coupled ?(like a freighliner Argosy)

  3. #3
    Join Date
    Oct 2014
    Location
    Australia
    Posts
    37
    Rep Power
    0

    Re: Vector 1850 overload code

    It happened over the weekend and I was having a look at it today. Doesn't say what actually
    Overloaded. Had fault I100 in fault list when I turned it on and report from driver on wknd just
    Said shutdown a couple of times with overload code.
    It's coupled under a Mercedes prime mover with plenty of breathing space. (B Trailer)
    Do the ground modules intermittently play up?
    Is there a correct procedure for testing the generator as when you test between line to ground
    There is continuity.
    What are the resistances for the compressor and generator ?

  4. #4
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: Vector 1850 overload code

    Alarm 100 is overload/ground fault. At least on an 1800. If it does have an OGF module, need to look at it if you catch it shutting down and see if the LED is on or off to determine if it shutdown on overload or ground fault.

  5. #5
    Join Date
    Oct 2014
    Location
    Australia
    Posts
    37
    Rep Power
    0

    Re: Vector 1850 overload code

    Caught it shutting down today.
    No LED on. Shutting down in Pretrip
    Test 2 after it had energised the comp
    Contractor and held in for a little while.
    Megger everything and tested everything
    Again. From generator L1,2&3 0.4 ohms
    To ground.
    Ten mins later started up ran and passed a pretrip
    No dramas. I'm thinking the OGF is faulty
    And I'll go over earthing connections

  6. #6
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: Vector 1850 overload code

    Quite possibly right.
    I have seen faulty OGFs before, and your description is almost exactly what I experienced.

    Replace OGF, job done!

  7. #7
    Join Date
    Mar 2009
    Location
    Indiana, USA
    Age
    56
    Posts
    75
    Rep Power
    16

    Re: Vector 1850 overload code

    I have also changed several OGF that were bad.