    regulation of suction pressure



    I am doing project for refrigeration cycle . I notice that the suction pressure is regulated by speed control of the compressors which are driven by Gas Turbines . Why is that ??

    What is the relation between condensing , evaporating temperature and suction pressure because I noticed from data that the speed control increases on afternoon(11 am -12 pm ) but at night or morning it decreases why is that ?

    Also , the suction flow rate is higher in the afternoon that at night or morning !



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: regulation of suction pressure

    Perhaps investigation of a temperature / pressure table for a refrigerant will help explain things for you.

    Also study a Mollier diagram of the process.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: regulation of suction pressure

    Quote Originally Posted by chemicalENG View Post

    I am doing project for refrigeration cycle . I notice that the suction pressure is regulated by speed control of the compressors which are driven by Gas Turbines . Why is that ??
    My knowledge of gas turbines is limited but I believe they are fixed speed?
    If the gas turbine is fixed speed the compressor duty will be fixed also?



    Quote Originally Posted by chemicalENG View Post
    What is the relation between condensing , evaporating temperature and suction pressure because I noticed from data that the speed control increases on afternoon(11 am -12 pm ) but at night or morning it decreases why is that ?
    Refrigeration is a relationship between temperatures and pressures
    inside a system and they are affected by temperatures outside the
    system.

    If the ambient is high it will effect the pressure temperature relationship,
    if the product around the evaporator changes in temperature that will place
    different loads onto the working system and pressure temperatures will change.

    Ask yourself what happened in the afternoon for there to be a change?
    Did the day warm up and put more load onto the system?


    Quote Originally Posted by chemicalENG View Post
    Also , the suction flow rate is higher in the afternoon that at night or morning !

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Nov 2014
    Location
    Bahrain
    Posts
    11
    Rep Power
    0

    Re: regulation of suction pressure

    Quote Originally Posted by Rob White View Post
    My knowledge of gas turbines is limited but I believe they are fixed speed?
    If the gas turbine is fixed speed the compressor duty will be fixed also?





    Refrigeration is a relationship between temperatures and pressures
    inside a system and they are affected by temperatures outside the
    system.

    If the ambient is high it will effect the pressure temperature relationship,
    if the product around the evaporator changes in temperature that will place
    different loads onto the working system and pressure temperatures will change.

    Ask yourself what happened in the afternoon for there to be a change?
    Did the day warm up and put more load onto the system?





    Regards

    Rob

    .

    The gas turbine is variable speed . On afternoon the speed increases .

    On afternoon there is two problem I guess : The temperature of air in air cooler and temperature of process feed gas in evaporator because it comes from longline pipes .Hence , in summer the temperature of gas entering the evaporator increases.

    Different load you means that the required refrigerant flow rate is changining depending on the temperature outside of the system ???

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: regulation of suction pressure

    Hi, chemicalENG

    Quote Originally Posted by chemicalENG View Post
    I am doing project for refrigeration cycle . I notice that the suction pressure is regulated by speed control of the compressors which are driven by Gas Turbines . Why is that ??
    What kind of project are you working on?
    I assume you have turbo compressor and speed control is used to control compressor capacity.



    Quote Originally Posted by chemicalENG View Post
    What is the relation between condensing , evaporating temperature and suction pressure because I noticed from data that the speed control increases on afternoon(11 am -12 pm ) but at night or morning it decreases why is that ?

    Also , the suction flow rate is higher in the afternoon that at night or morning !
    Evaporating temperature and suction (evaporating) pressure within evaporator are the same for refrigerant in question expressed in different way ... i.e. at saturated state evaporating temperature corresponds to evaporating pressure and v.v. you can check that in refrigerant charts for your refrigerant or for any other refrigerant ....

    Condensing temperature/pressure you can choose according to your system and your needs and of course it will change with changing of compressor capacity and evaporating pressure/temperature.

    Flow rate is different, because you have to have higher compressor speed to move more mass due to heat ingress from surrounding (long pipes, not good insulation or maybe just capacity increase within evaporator itself) ... we do not know anything about your system and all this is guessing, agree?


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    Nov 2014
    Location
    Bahrain
    Posts
    11
    Rep Power
    0

    Re: regulation of suction pressure

    Quote Originally Posted by Josip View Post
    Hi, chemicalENG



    What kind of project are you working on?
    I assume you have turbo compressor and speed control is used to control compressor capacity.





    Evaporating temperature and suction (evaporating) pressure within evaporator are the same for refrigerant in question expressed in different way ... i.e. at saturated state evaporating temperature corresponds to evaporating pressure and v.v. you can check that in refrigerant charts for your refrigerant or for any other refrigerant ....

    Condensing temperature/pressure you can choose according to your system and your needs and of course it will change with changing of compressor capacity and evaporating pressure/temperature.

    Flow rate is different, because you have to have higher compressor speed to move more mass due to heat ingress from surrounding (long pipes, not good insulation or maybe just capacity increase within evaporator itself) ... we do not know anything about your system and all this is guessing, agree?


    Best regards, Josip

    the project is about the relationship between gas turbine power and refrigeration effect in evaporator .

    how improving gas turbine power increases the refrigeration effect in summer !!

  7. #7
    Join Date
    Nov 2014
    Location
    Bahrain
    Posts
    11
    Rep Power
    0

    Re: regulation of suction pressure

    the process diagram almost like the attached image863408.fig.001.jpg

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: regulation of suction pressure

    Hi, chemicalENG

    Quote Originally Posted by chemicalENG View Post
    the process diagram almost like the attached image

    863408.fig.001.jpg
    Almost like ... that discrepancy (if) can change a lot at final outcome ....

    but let's try to do our best, at least ...

    Gas turbine we usually use to drive centrifugal compressors (with reduction gearbox also other compressors and other machines), but still we do not know anything in general about your plant ... is it possible to tell us something more about ... to be able to help you as much as possible.


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.