    Exclamation daikin error code UH



    Dear all,
    Pls give me a solution for this,
    I found UH error code on one fcu and A5 error code on another fcu. Both are connected to the same CU.(4mks80E)
    I have checked these things.
    Indoor outdoor compatiblity.
    Indoor outoor wiring and copper piping.
    Pls help me to figure out this issue.
    Is it pcb faullt fault.



  2. #2
    Join Date
    Nov 2013
    Location
    England
    Age
    37
    Posts
    18
    Rep Power
    0

    Re: daikin error code UH

    I think the A5 is a thermistor fault and uh is I wiring/ pcb with outdoor

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin error code UH

    A5 Operation halt due to the freeze protection function or high pressure control
    U4 Signal transmission error (between indoor and outdoor units)
    UH Improperconnection of
    transmission
    wiring between
    outdoor and
    outdoor unit
    outside control
    adaptor
    Last edited by install monkey; 14-01-2015 at 08:04 PM.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin error code UH

    lev's on outdoor are prone to sticking

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin error code UH


  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin error code UH

    From memory, Brian_UK had one of these faults a few years back - I think it's something to do with VAM'S.

    There again, I am probably wrong

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: daikin error code UH

    test cables are correct 1.2.3 corresponds with indoor 123 and check pipework isnt crossed ie unit A is piped to ports A and wired at port A terminals

  8. #8
    Join Date
    Jan 2009
    Location
    Canary Islands
    Age
    74
    Posts
    144
    Rep Power
    16

    Re: daikin error code UH

    If it's a system I've not seen before I will always carry out a wiring error check. Use SW3 on exterior service monitor PCB. This will confirm as Install Monkey as above.
    I've had UH a couple of times and it was a EEV coil each time. The EEV with a faulty coil does not shut and allows refrigerant to pass through an interior unit that is not in operation.