    Clivet wsat-xin 21-141 problem



    Hello! I am working clivet wsat-xin 21-141 for about 4 months now... Four days ago i had error007 shown... i deleted the alert as written in the manual and the pump started working again. After working for about 10 to 15 mins i have again the same error... Does anyone know smthing? Thank you!



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet wsat-xin 21-141 problem

    faulty pressure transducer or gas issues
    Last edited by install monkey; 11-01-2015 at 06:00 PM.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet wsat-xin 21-141 problem


  4. #4
    Join Date
    Jan 2015
    Location
    Greece
    Posts
    3
    Rep Power
    0

    Re: Clivet wsat-xin 21-141 problem

    thank you very much for the answer...we checked with the technician and there are no gas issues. maybe there is a faulty pressure transducer. I am thinkink also that maybe it is needed to make some changes at parameters.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet wsat-xin 21-141 problem

    any issues with the water circuit? sticking flow switch maybe

  6. #6
    Join Date
    Jan 2015
    Location
    Greece
    Posts
    3
    Rep Power
    0

    Re: Clivet wsat-xin 21-141 problem

    If there is sticky circuit do i have to replace it or is there something else to do?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet wsat-xin 21-141 problem

    check water strainer, maybe adjust the flow switch, check the paddle isnt bent or snapped, check it isnt catching on the sides of the pipe stabbing, check 1 bar standing water pressure

  8. #8
    Join Date
    May 2010
    Location
    Greece
    Age
    42
    Posts
    16
    Rep Power
    0

    Re: Clivet wsat-xin 21-141 problem

    Check the water circulation make sure that your strainer is clean, pump works properly also messure the heat exchangers pressure drop as reffered in the manual posted above (pages 23, 40 and 42) anyway your machine needs DP more than 20kPa and less than 80kPa or 0.4 Q(l/s) to dont have low saturation temperatures!! if your chiller has low saturation adjustable parameter DO NOT CHANGE IT before check all the above i wrote otherwise you will transform your maneurop compressor to nice fish aquarium!!!

    Good luck!!!

    ps1 dont forget to feed us back when problem is solved