    Spectrum SB 30 full of ***** but running in a vacuum
    I am working on a spectrum that has the rear unit disconnected. The unit has a newly rebuilt throttling valve on it and I just charged it. The unit is full of ***** but it is running in a vacuum. The high side pressure is stable around 135psi and the low side is in a vacuum. It is cooling but only at a -7* differential.
    11,025
    Re: Spectrum SB 30 full of ***** but running in a vacuum
    Is the rebuilt valve working?
    Feb 2009
    telford
    2,090
    33
    Drier,txv?
    Melbourne
    347
    check the LLS diode is energised on the relay board(liquid line solenoid) Bottom left corner of board.
    If it is, probably TX valve or power head fault
    Nov 2014
    Poland
    48
    12
    your problem most be found in the liquid line, check also if your LP-gauge is correct.
    Sep 2009
    Iran
    66
    672
    1
    all suggestion might be right,
    what is a your refrigeration gas ? why your hp pressure is a 135 psi
    if your using R-22 it should not be less than 180 psi , Min. TX valve works pressure to works and open correctly
    Melbourne
    347
    it'd be R404a , the OP should of posted in the TRANSPORT section.