    Will Reclaiming mix of Nitrogen Break Re-claimer



    Hi Guys

    I have an employee that has told me if you reclaim a mix of refrigerant with a mix of Nitrogen it will break the reclaimer . Has anyone heard of this i have done it many times before and never had any problems in fact we where taught to do this at Tafe. You can use a mix of Nitrogen and refrigerant to leak check a system so that it will be picked up with an electronic leak detector.

    Phill



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Will Reclaiming mix of Nitrogen Break Re-claimer

    Hi philthy
    I guess there is an element of truth in the statement.
    Given that Nitrogen is a non condensable gas, therefore if any is drawn into the reclaim unit it could cause problems.
    More likely the increased pressure that may exist could easily push a slug of Liquid through the Unit which is just as bad.
    Throttle the unit and proceed slowly and you should be OK.

    Trying to rush and pulling liquid is the normal killer. Despite the claims that most units shift Liquid.
    How much is the real question?
    Grizzly

  3. #3
    Join Date
    Oct 2013
    Location
    Australia
    Posts
    18
    Rep Power
    0

    Re: Will Reclaiming mix of Nitrogen Break Re-claimer

    Hi Grizzly thanks for your reply.

    It would be interesting to see what more people think as well especially everyone out there that will use a mix to locate with a digital leak detector.

    Thanks again Griz

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Will Reclaiming mix of Nitrogen Break Re-claimer

    Quote Originally Posted by philthy View Post
    Hi Grizzly thanks for your reply.

    It would be interesting to see what more people think as well especially everyone out there that will use a mix to locate with a digital leak detector.

    Thanks again Griz

    Before we new about the ozone layer & global warming etc, it was normal to put a bit of ***** in & pump up the pressure with nitrogen.
    Of course we never reclaimed it, we let it go to atmosphere.

    I can't practically see how you could do it if a reasonable amount of nitrogen was used.
    The discharge pressure of the reclaim would skyrocket, I would have thought.
    I would suggest these days higher nitrogen test pressure used to test after unit reclaimed.
    Some have suggested on this forum in the past to add helium & use something like Big BLue or soapy water to find leak/s.

  5. #5
    Join Date
    Oct 2013
    Location
    Australia
    Posts
    18
    Rep Power
    0

    Re: Will Reclaiming mix of Nitrogen Break Re-claimer

    Hi Ranger

    Dont get me wrong i would never put the ***** in after the nitrogen. This would only be in a situation where the system is short of gas not empty. You are adding the nitrogen to pump up the pressure so it is easier to find with a electronic leak detector. The gas is going to be reclaimed anyway for when you have to repair the leak.

    Phill

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Will Reclaiming mix of Nitrogen Break Re-claimer

    I think it would be ok until the head pressure got too high, you would likely need a big recovery cylinder to stop the pressure getting too high and also need to be careful not over pressure the recovery cylinder.
    Mostly found in Oxfordshire, UK :)