    Spectrum SB 30 full of ***** but running in a vacuum



    I am working on a spectrum that has the rear unit disconnected. The unit has a newly rebuilt throttling valve on it and I just charged it. The unit is full of ***** but it is running in a vacuum. The high side pressure is stable around 135psi and the low side is in a vacuum. It is cooling but only at a -7* differential.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Spectrum SB 30 full of ***** but running in a vacuum

    Is the rebuilt valve working?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Spectrum SB 30 full of ***** but running in a vacuum

    Drier,txv?

  4. #4
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: Spectrum SB 30 full of ***** but running in a vacuum

    check the LLS diode is energised on the relay board(liquid line solenoid) Bottom left corner of board.
    If it is, probably TX valve or power head fault

  5. #5
    Join Date
    Nov 2014
    Location
    Poland
    Age
    48
    Posts
    12
    Rep Power
    0

    Re: Spectrum SB 30 full of ***** but running in a vacuum

    your problem most be found in the liquid line, check also if your LP-gauge is correct.

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Spectrum SB 30 full of ***** but running in a vacuum

    all suggestion might be right,

    what is a your refrigeration gas ? why your hp pressure is a 135 psi

    if your using R-22 it should not be less than 180 psi , Min. TX valve works pressure to works and open correctly

  7. #7
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: Spectrum SB 30 full of ***** but running in a vacuum

    Quote Originally Posted by mbc View Post
    all suggestion might be right,

    what is a your refrigeration gas ? why your hp pressure is a 135 psi

    if your using R-22 it should not be less than 180 psi , Min. TX valve works pressure to works and open correctly
    it'd be R404a , the OP should of posted in the TRANSPORT section.