    Hi guys
    This is my first post just starting to get involved with refrigeration plant. just after some advice.
    what should the suction and discharge pressures be for a -18C deep freeze room running on R417a water cooled condenser?
    fes
    3,355
    Re: R417a Suction and Discharge
    fes,
    Can depend on how it was designed, but with maximumwater temp in at 29 deg C I would suggest between 9 to 12 bar or 30 to 40 deg saturated discharge temperature.
    Normally set at a desired pressure to cover summer conditions & pressure difference across TX valve so it performs as per design.
    What do you have at the moment & how is it controlled.
    Aug 2014
    75
    508
    Hi fes
    Has Ranger says discharge pressure around the 10 to 12 Bar should be OK and the suction around 0.5 Bar.
    But what type of expansion valve is on the job. If its a 404A , R22, or similar the suction will be lower as I don't know any manufacturer who makes an R417A expansion valve, and therefore the valve will not calibrate with the systems refrigerant pressure/temperature, normally resulting will a low suction guage and high superheats .
    If you have an electronic valve fitted it should run the suction around the 0.5 Bar mark
    Jan 2015
    uk
    5
    Cheers guys
    the inlet to the condenser is 25C and outlet is 36C
    TX Danfoss R22 -40/+10C PS34bar
    I seam to have stabled the discharge pressure at 14.5bar and suction is 0.6 bar.
    is there a formula for working out pressures for suction discharges? i.e to establish the amount of refrigerant to put into a system?
    Thanks in advance
    Fes
    3,355
    Quote Originally Posted by fessy View Post
    Cheers guys
    Thanks in advance
    Fes
    Maybe liquid line subcooling.
    Suction pressure several degrees below water out temp.
    Water in/out seems to much difference,
    Have you checked it & pump/strainer.
    Does the condenser have a pressure operated water control valve or something similar?