    Help?!



    Hey guys I have an open front bottle cooler that I'm working on, it is not cooling, compressor is running, refrigerant is at correct charge and all fan motors are running.
    Is this an expansion valve issue?

    Any input would be great.

    I have new expansion valve but want to get a second opinion before I fit new one. Need advice ASAP. Thanks.

    Hayden.



  2. #2
    Join Date
    Dec 2014
    Location
    Scotland
    Age
    31
    Posts
    2
    Rep Power
    0

    Re: Help?!

    Temp is also up around 22degrees C

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Help?!

    cond coil clear?
    comp pumping?
    adjust txv

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Help?!

    How have you confirmed the refrigerant charge is correct if the system is not cooling?

    For a underfeeding TEV you would expect to see a lower than normal suction pressure, a lower than normal head pressure and excessive ice formation on the TEV and possible the first part of the evaporator circuit (though defrosts may clear this)
    It can be underfeeding due to incorrect adjustment (unlikely in previously working system), the sensing bulb could have lost some or all of its charge making the valve shut down, or the inlet filter could be blocked.
    A blocked drier or failed solenoid can give similar symptoms as could mechanical damage to pipework.

    http://www.danfoss.com/nr/rdonlyres/.../pf000a102.pdf
    Last edited by monkey spanners; 28-12-2014 at 03:06 PM.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Help?!

    Good document. I'd spread the love but it seems someone thinks I don't have enough to go around, haha

  6. #6
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Help?!

    Hi Hayden
    There are many reasons why the fridge is not working, inefficient compressor, blocked drier, faulty TX, short of refrigerant, blocked condenser, iced evap to name a few.
    A bit more info would be helpful.
    The Danfoss link should help you sort it but if not give us some more info.

    Regards
    Paul
    Born to fish, forced to work

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Help?!

    Did you charge system in liquid phase or vapour phase. ?

  8. #8
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Help?!

    you wort comp. is running ,

    do you have heat on pipe goes to condenser and do you have cold on pipe is coming from evap.
    might one of your valve plate is broken and your comp. does not do any compress
    to understand you have to check your inlet and outlet pressure on the compressor .
    from that you will find the efficiency of compressor and also from touch of drier inlet and outlet of drier if there is different temp you will find is blocked and you have to change it .

    if you see the TX valve you will find is it working or not

  9. #9
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Help?!

    is this an open case deck ? - / an open integral fridge. maybe the obvious but is there an air replacement issue. i.e. an ac blowing into the cabinet or next to an entrance door?