    Panasonic multi split solid ice in heating



    Hi guys
    Got a quad 27 with full icing and won't do a defrost.
    No gas leaks line sets within limits.
    Ok till ambient now 0oc.
    Says will do a defrost every 4 5 mins or hitting -6oc.
    All frozen bar small section.
    Going back Monday to weigh out refrigerant and weigh in new.
    Could it be undersized ?
    Going to speak to panasonic on Monday but any help much appreciated.
    It's xmas and want to get it sorted for customer.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Panasonic multi split solid ice in heating

    .

    I don't know much about the make you are talking about
    but if it is freezing up you need to check if it is defrosting.

    If it is defrosting, then how often and for how long?

    If it is not defrosting then why?

    Look to the obvious before you start pulling out the refrigerant.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Panasonic multi split solid ice in heating

    before checking gas charge have you ran the unit in cooling to check rv actually operates?, if energised for heating - unplug it off the board

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Panasonic multi split solid ice in heating

    Coil temp sensor?
    Mostly found in Oxfordshire, UK :)

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Panasonic multi split solid ice in heating

    Is the drain from the condenser unit clear?

    A build up of ice at the bottom will climb the coil if it can't defrost properly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jan 2014
    Location
    shetland
    Posts
    18
    Rep Power
    0

    Re: Panasonic multi split solid ice in heating

    It doesn't do a defrost.
    Had it on cooling and it ran fine.
    Drain is clear so don't know why it won't do a defrost.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Panasonic multi split solid ice in heating

    do we have a model number for the outdoor?

  8. #8
    Join Date
    Jan 2014
    Location
    shetland
    Posts
    18
    Rep Power
    0

    Re: Panasonic multi split solid ice in heating

    Yes outdoor is cu-4e27.

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Panasonic multi split solid ice in heating

    https://drive.google.com/file/d/0Bz6...ew?usp=sharing
    service manual
    pg 23 shows sensor resistances (block circuit diagram)- bottom corner
    Last edited by install monkey; 29-12-2014 at 11:10 AM.

  10. #10
    Join Date
    Jan 2014
    Location
    shetland
    Posts
    18
    Rep Power
    0

    Re: Panasonic multi split solid ice in heating

    Pulled 2.6kg of refrigerant out today.
    Should have been 3.4kg.
    Vacced and leak tested on instalation.
    Leak tested last week.
    Vacced again today.
    Top coil was not freezing so was not able to hit defrost temperatures.
    Thought it would still defrost due to accumulated time and ambient.
    Can only think was short of refrigerant in manufacturing.
    Attached Images Attached Images