    heat pump split ac reversing valve question?



    Hi
    i noticed these different method of reversing valve operation in heating mode
    when u turn off the unit with remote control
    in some type you will hear whoosh of the RV valve once the unit shut off
    in other split ac the RV valve keep energized for 30 seconds after the unit shut off
    while in little type or ac
    the RV keeps energized till the circuit breaker is lifted
    so what is the advantage and disadvantage of energizing or de energizing
    sorry for broken English


    Power consists not in being able to strike another but in being able to control oneself when anger arises

  2. #2
    Join Date
    Oct 2014
    Location
    Ireland
    Age
    33
    Posts
    43
    Rep Power
    0

    Re: heat pump split ac reversing valve question?

    As far as i know there is no difference. Some units engerise rv on heating and de-energise on cooling. It all depends on manufacture. No advantage either way. I could be wrong!!!!

  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: heat pump split ac reversing valve question?

    thank u
    any more info
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  4. #4
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: heat pump split ac reversing valve question?

    Hi guys,
    It have been a long time i didn't lor or post, hoping this will be a good return.

    Some thoughts ....

    In large systems, the expansion device is thermostatic or else but not a capilary, those maintaining the RV activated for some time will allow the low pressure side to gain some pressure and the high pressure side to loose some pressure then they release the RV so they make the RV piston moves slowly to his initial place those avoiding fast mechanical operation and giving more lifetime to the RV.

    In systems using capilary the increase in the pressure at the low side and the decrease at the high side takes more time so they let it activated till the power is off.

    I might be wrong, this is just a point of view.

    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  5. #5
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: heat pump split ac reversing valve question?

    that was very useful info
    for most of mini split here
    are capillary type
    Power consists not in being able to strike another but in being able to control oneself when anger arises