    Liquid receiver size



    Dear friends,

    In your opinion, what's the best rule to size a liquid receiver for a big plant with ammonia?

    Volnei



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Liquid receiver size

    Volnei, have you tried this thread.....
    http://www.refrigeration-engineer.co...highlight=size
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Liquid receiver size

    Volnei,

    Another great question.

    As you have suggested this is for a big system I will not include a discussion or comments on full system pump down capability. The systems are simply becoming too large for this.

    The actual pump down volume would of course depend on the requirements of the system and the piping installation.

    If for example, the system was installed with the main liquid line feeding the whole facility; the pump down volume of the receiver would then be dependent on the largest possible volume that could be anticipated to be pumped down in the facility. Maybe a large flooded shell & tube chiller.

    The largest volume could also be a single area of the facility, say a large freezer or cooler (all of the evaporators in one of these areas).

    If different areas of the facility are fed liquid refrigerant off of the main line, any one of these areas could be selectively chosen as the pump down volume.

    Perhaps one of the low-side vessels has a larger liquid volume contained in it, rather than the evaporators. The vessel volume could then become a controlling factor.

    I don't think this is a question that has a single answer other than to say, it depends on the facility and installation.

    If the low-side vessels are provided with a sufficient design pressure (equal to the receiver) they could also be used for pump down service.

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Liquid receiver size

    Hi Guys

    What I have been taught is to size on the largest group of cooler to defrost at anyone time + the volume of the pumped liquid line

    Kind Regards. Andy

  5. #5
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: Liquid receiver size

    This is a intersting question. i have sized receivers from almost critical charge to huge.

    I think you have to consider the estimated liquid volume considering the coils at 20 percent, half of the volume of the lines and an additional amount %%%%.

    Normally i have found that the pump vessels can also be used for storage and usually are. The new regs are vaugue in the usa for how big, so I think you have to consider the plant the location, and OSHA. Good Luck

    At least the vessels are about the cheapest component in the big systems.

    bruce boldy

    i am now with Trane in the usa
    Refrigeration was more fun....

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Liquid receiver size

    Quote Originally Posted by BruceBoldy
    ...the estimated liquid volume considering the coils at 20 percent
    I would hesitate to use a blanket statement of 20% to be used for calculating the liquid volume. If the coils are flooded or bottom fed the hold up volume can be a lot higher.

    I also have a question.

    The new regs are vague in the USA for how big
    What regulations are there in the US that tell you how big the receiver has to be?

    The only thing I am aware of is the requirement for the receiver to have sufficient volume of at least 125% of the receiver holding capacity.

    100% would be the required storage volume for the refrigerant and the extra 25% is for the gas space for expansion.
    Last edited by US Iceman; 21-04-2006 at 02:17 AM. Reason: revised text

Similar Threads

  1. Liquid receiver
    By Renato RR in forum Fundamentals
    Replies: 134
    Last Post: 02-03-2011, 07:55 AM
  2. Replies: 2
    Last Post: 16-11-2005, 06:34 PM
  3. Liquid Receiver Calculations
    By David PS in forum Fundamentals
    Replies: 6
    Last Post: 08-04-2005, 09:55 AM
  4. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •